What are the possible causes of foaming in a waste heat boiler fitted to an effluent incinerator installed in a rendering plant.
INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Foaming
ER
RE: Foaming
Generalblr is correct, it is normally contaminants in the boiler water which cause foaming. Usually the contaminants are hydrocarbons but in your case it may also be organic compounds.
Pay attention also to the amount of dissolved solids in the boiler water.
I suggest you complete a thorough analysis of the makeup water, the feedwater in the feedwater storage tank and the boiler water. When the boiler is down for maintenance, it will have to be cleaned. An acid wash may be required.
I have seen instances where contaminants were getting into the feedwater makeup tank through the tank vents. There is also the possiblility of people inspecting the boiler being contaminated with hydrocarbons or organics on their clothing, boots, tools, etc.
Cleanliness, of the boiler and the feedwater, and control of the boiler dissolved solids will usually prevent foaming.