DISSOLVED OXYGEN IN BOILER FEEDWATER

DISSOLVED OXYGEN IN BOILER FEEDWATER

DISSOLVED OXYGEN IN BOILER FEEDWATER

(OP)
We have been obtaining higher than desired readings of dissolved oxygen within our boiler feedwater recently.  Tests of the level of dissolved O2 in the suction of the boiler feedwater pump is currently 5 parts per billion and at the discharge it is 10 parts per billion.  The question is:  What can cause an increase in the level of dissolved oxygen within the boiler feedwater as it works its way through the pump?

RE: DISSOLVED OXYGEN IN BOILER FEEDWATER

Your pump either has an air or water leak (I thought I read in your other post that the pump is cooled by raw water).  If the pump is operating above atmospheric pressure then an air leak is really not likely.

jproj

RE: DISSOLVED OXYGEN IN BOILER FEEDWATER

My Question is,

How are u measuring the Do2 in suction and discharge?

If there are no leaks then the possibility of increase in O2 content at the discharge may be due to the following reason.

1. If you are measuring continously using a sampling system then take care that the sample pressure inside the flow through chamber (for the discharge sample) is same as the pressure that of the suction sample (i.e from the deareator).

2. Based on my experience i can tell you that there would be drastic difference if you use two types of measurement (i.e inline instrument for one measurement and measurement by sample conditioning for the other)

3. Check for any leaks in the sample tubing.

RE: DISSOLVED OXYGEN IN BOILER FEEDWATER

I have seen installations where the pump suction can fall just slightly below atmospheric pressure. Not far enough to cause any particular operating problems, but just enough that a small amount of air is drawn in around the seal or packing.

RE: DISSOLVED OXYGEN IN BOILER FEEDWATER

PUMP SEALS ARE A COMMON PROBLEM TO AIR GETTING INTO THE CONDENSATE RETURN.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources