calculate transmission monopole
calculate transmission monopole
(OP)
We want to calculate above power transmission monopole. What is the accepted deflection? (Percentage of height). Where this deflection being mentioned (described) in ASCE Manual 72 ?
Can you help me.
Thank.
Can you help me.
Thank.





RE: calculate transmission monopole
It is understood different designers and manufacturers use different criteria to limit deflections. IE tangent pole ~ 10-12% of height, deadend end structures 2-3% or there abouts. This includes deflections due to foundation displacements and foundation rotations. This probably is not very helpful, but perhaps others can provide more definitive information.
M. Hansen
Seattle Utilities
RE: calculate transmission monopole
1- (L&H) suspention towers : 4.5% of height
2- Tension and D.E. towers : 2.5% of height
But there is no limitation for deflection in ASCE MANUAL No. 72 and 52.
H. Namiranian
RE: calculate transmission monopole
Thanks for any help.
RE: calculate transmission monopole
Of course, you will need to engage the services of a qualified geotechnical engineering firm to develop these predictions using p-y curves to model the soil. And you can generally forget the "rules of thumb" on pole embedment i.e. 10% of pole height + 3'. Embedment will have to be calculated based on the actual soil properties...
Please see FAQ731-376 for great suggestions on how to make the best use of Eng-Tips Fora. See FAQ158-922 for recommendations regarding the question, "How Do You Evaluate Fill Settlement Beneath Structures?"