Reliability of an existing stand-by power Generator

Reliability of an existing stand-by power Generator

Reliability of an existing stand-by power Generator

(OP)
I am currently working on a project taht calls for replacing an existing emergency generator unit with a loarge rated one.  This unit is anywhere between five to fifteen years old and has roughly 487 hours of runtime.
The problem comes in the fact that the unit has experienced several thermal trips cause by personall trying to run too much on an older unit.  The unit runs for roughly 30 minutes before any trouble signs show up.  I was wondering if there are anyways/test that can be performed to ensure the alternator still functions properly and there are no residual effects on this unit?

RE: Reliability of an existing stand-by power Generator

Contact the generator manufacturer. They have peocedures for inspecting and testing the generator utilizing load banks.

RE: Reliability of an existing stand-by power Generator

What is the capacity of your generator and what is the load you are pulling ? Since you mentioned replacing with a bigger genny, may be you are overloading the present one and causing thermal trip?

RE: Reliability of an existing stand-by power Generator

When you say thermal trip, do you mean the output circuit breaker tripped or was it actual winding overtemp?

If it was just tripping of the circuit breaker, check that it is set correctly (if adjustable). You may want to have the circuit breaker tested. If you suspect thermal damage to the generator, you might want to do an insulation resistance test test. As Hertz said, consult the manufacturer.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources