Torsional capacity of SHS/RHS Section
Can anyone tell me how I can approximate with reasonable accuracy the torsional capacity of a SHS/RHS Section?
Torsional capacity of SHS/RHS SectionTorsional capacity of SHS/RHS Section(OP)
Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesWhat is rapid injection molding? For engineers working with tight product design timelines, rapid injection molding can be a critical tool for prototyping and testing functional models. Download Now
The world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
RE: Torsional capacity of SHS/RHS Section
In Australian practice, the design torsional moment section capacity is calculated thus:
phi*M_z = phi*0.6*f_y*C
where:
- ‘phi’ is the capacity factor, equal to 0.9 [dimensionless]
- ‘M_z’ is the unfactored torsional moment section capacity [kNm]
- ‘f_y’ is the yield stress used in design [MPa]
- ‘C’ is the torsional section modulus [mm3]
For rectangular and square hollow sections:
C = (t^3*h/3 + 2*k*A_h)/(t + k/t)
where:
- ‘t’ is the wall thickness of the section [mm]
- ‘h’ is the length of the mid-contour, h = 2*[(b - t) + (d - t)] – 2*R_c*(4-pi) [mm]
- ‘A_h' is the area enclosed by ‘h’, A_h = (b – t)*(d – t) – R_c^2*(4-pi) [mm^2]
- ‘k’ is the integration constant, k = 2*A_h*t/h [mm^2]
- ‘b’ is the overall width of the section [mm]
- ‘d’ is the overall depth of the section [mm]
- ‘R_c’ is the mean corner radius, R_c = (R_o + R_i)/2 [mm]
- ‘R_o’ is the outer corner radius [mm]
- ‘R_i’ is the inner corner radius [mm]
- pi = 3.142
The design check is:
M_z* < phi*M_z
where:
- 'M_z*' is the design torsional moment (ultimate limit state)
AISC also has desin guide for torsion availble
Check it out at
www.enercalc.com
They have a full function demo you can try before you buy.
It is definitely worth its cost to any practicing structural engineer.