Looking for Solenoid Valve
Looking for Solenoid Valve
(OP)
I am trying to find a bi-stable solenoid valve which is approved for natural gas. For my application, it is important that the valve not consume power unless it is opening/closing. Has anybody come across anything like this?





RE: Looking for Solenoid Valve
I believe that with a bistable design, you will not find a AGA, CGA or equivalent certification. The reason being the failure mode is not set. You probably only need concern yourself with Explosion Proof coils and a manufacturer's fluid compatibility recommendation.
RE: Looking for Solenoid Valve
ISO size1 solenoid? EB-solenoid? F-solenoid?
with or without auxiliar pilot air?
write to me at most@isb.perd.net.pk
RE: Looking for Solenoid Valve
RE: Looking for Solenoid Valve
RE: Looking for Solenoid Valve
The main issue here as ghillis stated above certification will be difficult because of the fail safe mode. However if the valve ports are not very large other approaches may provide a solution for your application.
Please visit www.vitrom.com for more info.
Contact me at Reis@vitrom.com