CQM1 Downloading Problem
Message: Cannot download the program. UM is protected.
PLC Software/Hardware:
a) CX-Programmer v3.10
b) CQM1-CPU11
c) CQM1-CIF02
Note: CPU Dip SW 1 is OFF (When is On I get the same result)
1) I click “Go online” icon.
2) Message “About to connect to the PLC. Do you wish to continue” OK
3) I click “Transfer to PLC/Download” icon.
4) Window with download options appear. Program only is selected.
5) Message “This command will affect the state of the connected PLC. Continue?” OK
6) Message: Cannot download the program. UM is protected.
Please advice, what could be a problem?
Dan
b) CQM1-CPU11
c) CQM1-CIF02
Dan
RE: CQM1 Downloading Problem
Have you tried using SYSWIN the older omron plc software, do you get a similar message.
Ultermatly I would say call 0870 752 0861 and speek to the OMRON guys they seem to have one of the best PLC service and support lines of any OEM
Go to the PLC menu, then Protection, then Release Password. The password will be four digits.
If you can't figure it out reply and I will get online with a PLC and figure it out again.