Parallel operation of Utility to generator via LV distribution
Parallel operation of Utility to generator via LV distribution
(OP)
Hi all,
I would like to get some feedback on paralling substations.
We have the following substation operation and configuration:
- 13.8 kV Generator (12MW) capable of tying to Utility grid at the 13.8 kV level
- Misc double ended substations (13.8kV - 480Y) with sync relays.
We had the following scenario: The Generator-Utility Tie breaker was not able to close due to control wiring problems.
Question: Could I have transferred the loads of the double-ended substations (the ones that have sync relays) by paralling the two sources (Gen/Utility) without any impact to the electrical system?
Non-issues: double-ended substations are matched and substation gear is properly rated.
Issues/Concerns: Can I damage/impact the distribution system by tying the Gen-Utility via the 480V system? Will the Gen stay sync'd to the Utility or will there be current swings in the 480V system due to the generator trying to pick up load?
Personally I think evertything should be alright .... but you never know ....
Thanks for any input/suggestions y'all can provide.
I would like to get some feedback on paralling substations.
We have the following substation operation and configuration:
- 13.8 kV Generator (12MW) capable of tying to Utility grid at the 13.8 kV level
- Misc double ended substations (13.8kV - 480Y) with sync relays.
We had the following scenario: The Generator-Utility Tie breaker was not able to close due to control wiring problems.
Question: Could I have transferred the loads of the double-ended substations (the ones that have sync relays) by paralling the two sources (Gen/Utility) without any impact to the electrical system?
Non-issues: double-ended substations are matched and substation gear is properly rated.
Issues/Concerns: Can I damage/impact the distribution system by tying the Gen-Utility via the 480V system? Will the Gen stay sync'd to the Utility or will there be current swings in the 480V system due to the generator trying to pick up load?
Personally I think evertything should be alright .... but you never know ....
Thanks for any input/suggestions y'all can provide.






RE: Parallel operation of Utility to generator via LV distribution
Also, if you are exporting power to the utility, it is now going through two transformers that may not be rated for the load.
RE: Parallel operation of Utility to generator via LV distribution
If you only want to parallel briefly for the purposes of a non-interrupted transfer to generator, this should be possible. You will need a good quality and properly configured sync check relay and a means to match voltage. Also, you should have reverse power relays.
Your utility company no doubt has protective relaying requirements for this type of operation that would need to be met.
RE: Parallel operation of Utility to generator via LV distribution