which one to use, when and why?
have a generator off for a scheduled outage and moisture/humidity to high for Hi-Pot. would El-Cid provide condition in place of Hi-Pot?
have a generator off for a scheduled outage and moisture/humidity to high for Hi-Pot. would El-Cid provide condition in place of Hi-Pot?






RE: Hi-Pot & El-Cid
RE: Hi-Pot & El-Cid
as an alternative to not doing anything i was thinking at least an ElCid might give us info on the core if it can be done under high moisture/humidity conditions.
RE: Hi-Pot & El-Cid
An RSO is another test which you could reasonably carry out, although when you ask about El-CID in high humidity, you may as well ask 'em about an RSO too.
Out of interest, where are you?
RE: Hi-Pot & El-Cid
i am currently working for a client in the US that has plants accross the country.
RE: Hi-Pot & El-Cid
http://www.vpuc.com/minutes/r102300.htm
for:
The additional test (EI CID) is to verify the condition of the insulating material on the stator (unit was installed in 1954).
RE: Hi-Pot & El-Cid
http://www.engnetglobal.com/search/companylist.asp?bran...
http://www.adwel.com/elcid.html
etc. for more info on EL CID.
RE: Hi-Pot & El-Cid
there was no other concern for generator problems and none existed before it came down for the scheduled turbine outage.
RE: Hi-Pot & El-Cid
EL-CID test would not tell you anything about the insulation only tells you if you have a core problem.
RE: Hi-Pot & El-Cid
ELCID test checks the core only.