Boiler Blowdown Vessel Design
Hi all,
I was given a task to re-design a boiler blowdown vessel. The information that I was given with regards to the inlet condition is very limited.
I checked the standards on this iem and found out that the vessel must not hold more than 35 KPa of pressure.
I could be lazy and draw an exact replica of the existing blowdown vessel but that would be unprofeshional.
I guess my main concern is to make sure that my vessl will be able to operate at below 35 KPa. What information & calculations do I need to compute to ensure that my vessel falls within the regulation?
RE: Boiler Blowdown Vessel Design
I'd suggest you look at ASME Section VIII, Div.1. This is an internationally recognised code for the design and manufacture of pressure vessels. Although your vessel has a very low operating pressure, this code may be used.
John
Some tank vendors ( e.g. Keystone tank)still use this older code and will size the tank for you if you specify some basic information of the boiler.
Some issues that are not well covered by the older code:
a) for 3 pressure level HRSG's, the assumption that only 1 drum blows down at a time is not valid.
b) For HRSG's, with less than 10 ft gravity head from bottom headers to blowdwon tank NWL, it is possible to cause backflow into the reheater lower headers due to the reheater at vaccuum during cold startup and tank pressure at 10 psig.
c) for high presure units, you need to specifically calculate the max casualty flow through the HP superheater drains to the tank and ensure the tank wil not be overpressured and increase vent diameter accordingly.
We replaced the blowdown tank and vent stack on our old boilers (the original BD tank and vent stack were inside the main building -- 1950's vintage; we moved them outside) -- the welders got ahead of us and started sticking the stack up -- I had them stop and hold off until we finished the stack support design -- the vent stack was to be supported independently from the tank and to allow for pipe expansion (hung with spring supports)-- the welders just assumed the stack would be supported by the tank and a couple fixed supports along the way...
and this is what I think I'm going to do. If I can get a boiler detail I'll ring the manufacturer and see if they can give me some detail with regards to the blowdown condition.
If the manufacturer can't help me out I'll just measure the temperature at a few different point on the existing vessel eg. at the inlet pipe, a few reading s on the actal vessel and the outlet pipe. Then the steam chart should be able to tell me the coresponding pressure at those points. By doing so I should know straight away if I need to increase the size of the vessel or not.
If any one have a better method of sizing up a pressure vessel please let me know.
PS. Don't warry Pablo2 I got the vent stack under control.
There is an old victorian workcover document on blowdown tank sizing and calculations etc. I can send you a copy if you wish.
Bogu.
It would be great if you can forward the Workcover document to me. I have been looking up current workcover site but I cant find anything helpful. My e-mail address is yothd@yahoo.com.au.
Hi
Please send the document to nsurya@stantec.com