Siemens Simantic S7-200
Siemens Simantic S7-200
(OP)
Is there any way that the power supply module can be monitored for increase in current consumption, proir to a cabling failure. this would be due to cable routing in outside conditions. I have evidence that moisture is finding its way into the Nodes and destroying the cable interface with the node.
I also need some advice on how to introduce a text message display to notify a fitter of a node failure, Any adive on how this could be done would be extremly helpful.
Cheers.
Dave Brough
Eng.Tech. MIIE(elec)
I also need some advice on how to introduce a text message display to notify a fitter of a node failure, Any adive on how this could be done would be extremly helpful.
Cheers.
Dave Brough
Eng.Tech. MIIE(elec)





RE: Siemens Simantic S7-200
It would take a little design or trial and error work but you could design a shunt (if it's a DC fed power supply) that yields a low current (something in the 5-8mA range) at normal power supply load. Put the shunt in series with the incoming DC power lead and feed both sides of it to an AI. You would then have an analog representation of the PS load.
Alternatively, if the PS is fed by AC power, you might want to look into a small AC current transmitter to do the same thing. Either way, getting the PS load to be represented by an analog signal is a good way to monitor PS load.
The TD should be easy to configure once you figure out how to make the PS load an analog signal. Just trip a bit corresponding to a message in the TD.
I'll be interested to see if you can do what you want to do (monitor cable condition). Is the cable a Comm cable? or a signal cable?
RE: Siemens Simantic S7-200
That kind os PS you can get all information you need.
Best regards
Paulo Afonso
RE: Siemens Simantic S7-200
Right now I have the 216 operating a home solar heating system. I programmed it with MicroWin 3.2, I have a couple of OP3's & Protool Pro. I have been able to program the SCREENS I want(4 analog temperatures & status), but am unable to get the PLC to send the analog values OR status bits to the OP3.I use port 0 for the programming & want to use port 1 for the HMI.
Do I have to write a communications routine in the PLC to accomplish this?? The books aren't much help & so far I'm lost.Just a bit of experience would Help please. tnx Harold
RE: Siemens Simantic S7-200
You will need a RS232 cable like reference SIEMENS C79451-A3437-B122, (DB 9 FEMELE AND RJ-45).
My address is paulo.afonso@einaus.pt
Paulo Afonso
Integration expert
EINAUS Eng, Lda
Portugal