DRY EVAPORATOR RATING CONVENTION

DRY EVAPORATOR RATING CONVENTION

DRY EVAPORATOR RATING CONVENTION

(OP)
Hello fellow knowledge seekers,
We make custom hvac/refrig. system dedicated for particular close tolerance lab conditions. We match a ceiling mounted evaporator to the room load and to a Copeland condensing unit that has compressor, condensor, receiver pre-assembled.
The evaporator coil manuf. rate there coil at (x) btuh per
10 degree F. delta T.  This gives a slope to a line we draw on the particular compressor curve chart.  We then make sure we pick up the room heat load under this (capacity(y) to temp.(x)) compressor curve.
Now, I am told that this 10 degree delta T is the difference between the liquid suction temp in the coil and the room condition (coil EAT).  I was wondering why the delta is not the difference between the liquid suction and the leaving air temperature (LAT) from the air handling coil. Does this have something to do with LMTD which I kinda recall from heat transfer?  Most people here think I'm being anal about things. Thanks, friends.   

RE: DRY EVAPORATOR RATING CONVENTION

lippy: You said, "Now, I am told that this 10 degree delta T is the difference between the Refrigerent suction temp in the coil and the room condition (coil EAT". This is correct! To get the MTD you take the room temp. minus the Refrigerant (suction temp) and air off the coil minus the refrigerent(suction) temp add them togather and devide by 2. This gives you the MTD

RE: DRY EVAPORATOR RATING CONVENTION

One more thing low temp rooms (boxs) run at a 10 * TD where as Air conditioning coils usually run a 15*F TD coil

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources