I would like to know some manufacturers of line monitoring equipment for instrumentation signal lines. For instance, I would like to know when the line that carries the 4-20A signal from a field transmitter has broken.
Best,
Marc Assunpcao

RE: Line integrity monitoring - SIS Design

All of the TMR systems such as HIMA, ICS Triplex, Triconex, ABB August Systems, Siemens Quad Log as well as Trip Alarm out of Florida and various fire and gas detection system manufacturers.  Search for "supervised I/O".  This also applies to discrete devices but you would need some resistive device at the field instrument to differentiate a broken wire from an open contact.

John

RE: Line integrity monitoring - SIS Design

I thought the whole idea of a 4 to 20 mA loop is that an open circuit gives you 0 mA so you have built in open cct detection.  If the broken wire grounds out the circuit will overrange.  Either way the fault gets picked up.  I must be missing something.

RE: Line integrity monitoring - SIS Design

sjohnr is correct.

Whether 3-15 psig or 4-20 mAdc, the below scale reading of an elevated zero helps to identify problems.  The 0 mA signal can indicate a transmitter failure, a wiring problem anywhere in the loop or a failure within the monitoring electronics such as the I/O module or other processor, etc.  The below scale reading is easily detected and alarmed.  This is among the reasons to use an analog instrument for shutdown measurement where digital devices were previously most common.

Supervisory techniques exist to monitor the wiring for the discrete signals that differentiate the wiring malfunction from the contact opening.  This still does not identify a diaphragm failure that could prevent a pressure switch from functioning when demanded.

With a sigle transmitter, the TMR or quad systems differentiate the field side failure from the I/O or logic system failure.  Other techniques would be required to differentiate the transmitter failure from the open wiring.  I think that some TMR systems may have diagnostics that can make this differentiation too.

John

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources