Natural gas piping in plenums

Natural gas piping in plenums

Natural gas piping in plenums

(OP)
Occasionally we have to run natural gas piping above the ceiling in return air plenums.  This has come up recently in a couple restaurants.  Can't find a code limitation.  I recall in the past using welded pipe in this application.  Does anyone have any thoughts?  Thanks.

RE: Natural gas piping in plenums

As I recall, NFPA has an exception that allows this.

RE: Natural gas piping in plenums

I would suggest corrugated stainless steel tube, CSST.  It is available in many sizes and runs up to 250'.  No joints in the plenum.

RE: Natural gas piping in plenums

In the UK this is acceptable as long as the plenum serves only the room in which the gas is used.

Brian

RE: Natural gas piping in plenums

"Gas piping inside any building shall not be run in or through an air duct, clothes chute, chimney or vent, ventilating duct, dumbwaiter (like there are a lot of these days), elevator shaft or concealed plenum."

RE: Natural gas piping in plenums

A little more info from NFPA

A.6.2.5 It is the intent that gas piping, shutoff valves required by this code, and regulators be allowed to be installed in accessible portions of plenums, accessible ducts used to supply combustion and ventilation air in accordance with Section  5.3, and accessible spaces between a fixed ceiling and dropped ceiling.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources