(OP)
Does any of the experts in the protection field, who have more experience than myself know of a scheme to detect phase-phase faults on a unearthed system?

Thanking yous

RE: Phase-phase fault detection

A plain overcurrent relay (50/51) will do if there is no regards for fault direction.

God bless!

RE: Phase-phase fault detection

If instantaneous pick up is set correctly, it will help discriminate between short and overload.

For directional discrimination use device 67 in conjunction with 51 device.

RE: Phase-phase fault detection

A perfect application for negative sequence sensing.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources