generator sync problem

generator sync problem

generator sync problem

(OP)
Synchronised a 700 Kwatt steam turbine driven generator, (480v) to the utility with peculiar results...the voltage went to 510 volt the PF to about 0.2 the current to 900 amp with little indication of real power on the wattmeter before tripping on overcurrent. The excitation is provided through a Basler power factor controller and voltage regulator arrangement.
Any explanations on reason for above truly appreciated.

RE: generator sync problem

sounds like bad exciter/ AVR.
Powr factor controller is a static exciter ? I know excitation affects the power factor, but is this a real exciter?

Has this unit independelty run suscessfully on load?

RE: generator sync problem

Check the polarity of the CT used by the voltage regulator for PF control.  It sounds as though you have something mis-wired going the VR.  

RE: generator sync problem

un421ate1,

An ac machine, immediately upon synchroniztion with grid, will either take current from the grid (reverse power) or supply megavars with a low pf. Immediately upon synchroniation, your governor should control your unit to supply rapidly a minimum power of 10 to 20% to the grid.

RE: generator sync problem

New or older installation?  

RE: generator sync problem

(OP)
thanks for suggestions, generator currently on line synched to utility, acting normally..In island mode Basler power factor controller redundant, excitation provided by AVR, I guess the question I'm asking is would the symptons described be caused by under-excitation or over-excitation.
My boss doesn't like me experimenting.

RE: generator sync problem

Suggestion to the previous posting: It might be either of those two, under-excitation or over-excitation. Was PF=.2 lagging or leading?

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources