Synchronised a 700 Kwatt steam turbine driven generator, (480v) to the utility with peculiar results...the voltage went to 510 volt the PF to about 0.2 the current to 900 amp with little indication of real power on the wattmeter before tripping on overcurrent. The excitation is provided through a Basler power factor controller and voltage regulator arrangement.
Any explanations on reason for above truly appreciated.
Any explanations on reason for above truly appreciated.





RE: generator sync problem
Powr factor controller is a static exciter ? I know excitation affects the power factor, but is this a real exciter?
Has this unit independelty run suscessfully on load?
RE: generator sync problem
RE: generator sync problem
An ac machine, immediately upon synchroniztion with grid, will either take current from the grid (reverse power) or supply megavars with a low pf. Immediately upon synchroniation, your governor should control your unit to supply rapidly a minimum power of 10 to 20% to the grid.
RE: generator sync problem
RE: generator sync problem
My boss doesn't like me experimenting.
RE: generator sync problem