'n' on Dyn11 transformers?

'n' on Dyn11 transformers?

'n' on Dyn11 transformers?

(OP)
Please tell me what the 'n' stands for on a Dyn11 vector group transformer.

RE: 'n' on Dyn11 transformers?

n -> neutral

The neutral point is brought out of the transformer tank.

God bless!

RE: 'n' on Dyn11 transformers?


FWIW, in ANSI parlance it would be the "X0" terminal on a ∆-Y transformer.
  

RE: 'n' on Dyn11 transformers?

An in ANSI parlance, it would have the Wye on primary and the Delta on the Secondary to have the primary lead the secondary by 30 degrees.

RE: 'n' on Dyn11 transformers?


davidb --  So noted.  My mistake.
  

RE: 'n' on Dyn11 transformers?

busbar,

Not necessarily a mistake. If the transformer is a step up transformer, it would be the X0 terminal, and the H0 terminal on a step down transformer.

RE: 'n' on Dyn11 transformers?

If I remember right, when there is no 'n' in the vector group designation, e.g. Dy11, the neutral is not brought out (not accessible for use). When there is an 'n' in the vector designation the neutral terminal 'n' or 'X0' is available.

Please correct me if I am wrong!

God bless!

RE: 'n' on Dyn11 transformers?

When we mention to n in vector group ,it means that the neautral is brought out and earthed

RE: 'n' on Dyn11 transformers?

Suggestion: The neutral n is grounded, which implies one of various system grounding schemes

RE: 'n' on Dyn11 transformers?

The "n" stands for the neutral being brought out of the transformer tank and being available for current measurement or for being earthed. If "n" is absent from DYn11 that means it is an isolated neutral Delta-wye Xmer

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources