Effect of reinforcing on UL fire ratings

Effect of reinforcing on UL fire ratings

Effect of reinforcing on UL fire ratings

(OP)
A composite slab design for a hospital in California has been reinforced for diaphragm forces using #4 at 16 e/w. The UL design quoted (D916) called for 6x6/10x10 mesh. The design replaced the mesh with the rebar. The fire marshal says this design does not meet the UL requirement because the rebar is diferent than the mesh. Does anyone have a reputable source that adresses the effect of reinforcing on fire ratings?? UL is no help, they want to thicken the slab  by the difference in reinforment diameters???

RE: Effect of reinforcing on UL fire ratings

I think you're stuck thickening the slab or reverting to the mesh (yuck!).  The issue is thermal conductivity, not structural equivalence.  Steel conducts heat much better than concrete does -



Please see FAQ731-376  by VPL for tips on how to make the best use of Eng-Tips Fora.

RE: Effect of reinforcing on UL fire ratings

To meet the UL rating, you must provide exactly the same detail that was tested.  However, I do seem to remember that there are calculation methods that can be used to figure out the fire rating that can be assigned to the slab.  I would contact either NFPA, ACI or PCA (or all three) and find out the details on the method.

BUT, if it is a UL rating you MUST have, then you are stuck with meeting the EXACT requirements of the UL rating.

After some of the tragic fires around the country this summer, I can see why the Fire Marshal's are getting picky.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources