Recirculated Liquid Overfeed

Recirculated Liquid Overfeed

(OP)
When I'm sizing my suction lines, what is the proper way to compensate for the recirculation ratio in the evaporator?  Are you supposed to multiply the tonnage by the recirculation rate  and then fit your line to the new tonnage.  The line sizing charts I have are extremely vague

RE: Recirculated Liquid Overfeed

I'll assume you interested in suction line back to the compressor instead of the line from the low side receiver to the pump. You size the suction line using your design evaporator loads, and not the refrigerant flow thru the overfeed coil.  The recirc ratio influences coil rating, but you only need to account for the vapor flow leaving the evaporator for suction line sizing.  And the coil rating is what you need here.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources