INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login

HANDLE


PASSWORD
Remember Me
Forgot Password?

Come Join Us!

  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • Turn Off Ad Banners
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

E-mail*
Handle

Password
Verify P'word
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Partner With Us!

"Best Of Breed" Forums Add Stickiness To Your Site
Partner Button
(Download This Button Today!)

Member Feedback

"...I love the structure of the site. You start at the top, and drill down to what you want. Maybe I've been using Unix too long... :-) "

Geography

Where in the world do Eng-Tips members come from?
siena (Electrical)
22 Oct 03 16:41
I'm accustomed to spec'ing circuit breakers so that the downstream breakers have a shorter delay than the upstream (main) breakers.

But what do I do when I have a load with a high inrush current?  I pretty much have to use a breaker with the longest available delay for that load, so I won't be able to make the main breaker delay curve any longer.  I risk tripping the main breaker before the branch breaker.  

Can anyone shed any light on this?
Manindemand (Electrical)
22 Oct 03 19:36
What type relays do you have?

If you have micro-processor relays you can set your coordination pretty tight.  You can set logic in the main relay to block tripping as long as the feeder is timing out.  You would need a 2 conductor cable from the feeder to the main so the feeder can send the block trip signal to the main.  
rbulsara (Electrical)
22 Oct 03 20:23
Coordination is often a trade off between competing goals and compromises are almost unavoidable so do not feel bad about it.

Since a ground fault is more likely to happen than a 3 phase bolted fault, one of the ways to minimize mis-coordination is to provide ground fault relays which are much easier to coordinate by setting low pickup and fast time for the downstream breaker. If required, you can employ zone interlocking as suggested by 'Manindeman'. ( I am not crazy about zone interlockings).

By the way what type of breaker, trip units, current and voltages are you talking about here?.

dede61 (Electrical)
23 Oct 03 2:37
There are existing numerical protection relay who can take in account the inrush current of tranformers.  Like suggested by "manindeman" interlocking with blocking signals is a common way in this case to prevent tripping of the main feeders.

regards,

Danny
siena (Electrical)
23 Oct 03 9:14
Thanks for the tips, all of you.

This is probably a much smaller, simpler application than you are accustomed to.  The supply voltage is 120/208 and the main breaker is 100A.  One of the loads is a 3-phase air conditioner that draws 46A steady state and 239A locked rotor.

The breakers are basic magnetic type with fixed delay curves (they are not programmable).
dede61 (Electrical)
23 Oct 03 9:46
In that case selectivity is normaly made using B-C or D curves

regards,

Danny
rbulsara (Electrical)
23 Oct 03 12:39
The AC unit cutsheets usually have maximum OCPD rating on it (fuse or brekaer), indicated by MCB or MCF, just use that rating.

You can not coordinate any breaker or fuses with less than 2:1 ratio, more so with breakers.

You may forget about coordinating this one, as you will need minimum of 60A breaker. It will not coordinate with a 100A breaker.
Borti (Electrical)
23 Oct 03 13:03
You can specify a molded case circuit breaker (MCCB) equipped with a solid state trip unit having short time delay feature as the main breaker.
The branch breaker can be a MCCB with a thermal-magnetic trip unit, possible with an adjustable magnetic trip (usually between 5 and 10 times pug rating).
The selectivity between these two breakers is possible, as the short time pickup and delay can be adjusted on the main breaker. The only concern is the instantaneous override typical for MCCB's. The manufacturer should be consulted regarding the current value. You may have fault level below this value, in which case you would have acceptable selectivity.

Start A New Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Promoting, selling, recruiting and student posting
are not allowed in the forums.
Posting Policies

LINK TO THIS FORUM!
(Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum)
TITLE: Electric Power & Transmission & Distribution Forum at Eng-Tips
URL: http://www.eng-tips.com/threadminder.cfm?pid=238
DESCRIPTION: Electric Power & Transmission & Distribution technical support forum and mutual help system for engineering professionals. Selling and recruiting forbidden.