source / supplier for 13,8 kV contactor

source / supplier for 13,8 kV contactor

source / supplier for 13,8 kV contactor

(OP)
I cant find a source for 13,8 kV MV contactors. Who knows?
Are contactors available or do I need to use circuit breakers? We have high switching sequence and that is the reason why I would prefer contactor.

RE: source / supplier for 13,8 kV contactor

Hello Difference,

There's a bunch of manufacturers & suppliers out there, in fact to many to list here.

Would suggest you go to www.google.com and type the search text:

"MV Switchgear"
"HV Switchgear"
"MV Contactors"
"MV Circuit Breakers"
"HV Contactors"
"HV Circuit Breakers"

Then repeat the exersize using the words Medium Voltage and High Voltage in place of MV and HV in the above.

Regards,
GGOSS

RE: source / supplier for 13,8 kV contactor

Hello Difference,
I have in front of me a catalog of Schneider.  Look at http://www.schneider-electric.com/
They do from 3 to 24 kV.
Contactor up to 15kV are rated  400Amps and withstand about 10kA
The ones suitable for 24kV are rated 250Amps and can interrupt 25kA.

You can have these in cells with or without fuses.

I had a project on dedusting of an ore breaker plant.  The main fan was "only" a 1350kWatt 6kVolt motor.
There was no question about any high switching pace at all.  The motor manufacturer had set an interval of 2 hours between starts.
Furthermore launching the machine which, I admit, was coupled to an enormous fan wheel, was a painstaking and scary operation, even with a softstarter in the line.  We needed to call and ask permission to several plants in the neighbourhood before we could launch the machine and draw a mere 600Amps at 6kV during a minute or so.
I wish you all the best.

Best regards

RE: source / supplier for 13,8 kV contactor

Toshiba. A lot of the other ones you will find are brand-labeling Toshiba anyway.

http://www.tic.toshiba.com/

Quando Omni Flunkus Moritati

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources