corrosion protected pipe structure absorbs 2,500 amperes

corrosion protected pipe structure absorbs 2,500 amperes

corrosion protected pipe structure absorbs 2,500 amperes

(OP)
I have an instance where a pipe system with cathodic protection was the return path for a 2,500 ampere (estimated) surge.  Is it usual to have over-voltage, lightning, or surge protection on CP generation transformers or rectifiers?

Thanks for any feedback!

RE: corrosion protected pipe structure absorbs 2,500 amperes


only if you want to protect them, but the reality is that because you are dealing with such low dc volates about the only recourse is proper grounding and overvoltage protection

RE: corrosion protected pipe structure absorbs 2,500 amperes

(OP)
Hacksaw,
Thanks for the feedback.

Is the overvoltage likely to be able to sink 2,500A?  The agencies involved haven't located the low impedance return path for the current blast.  The CP generator was not damaged in this instance and was reported to be in continuous operation.

Any clues about where 2,500A could be absorbed in 0.1 seconds in a natural gas pipe system?

RE: corrosion protected pipe structure absorbs 2,500 amperes



Likely that the surge made it to ground before getting to your power supply. This is not surprising with impressed current designs; however, you should still design for over-voltage protection and proper equipment grounding.
 


RE: corrosion protected pipe structure absorbs 2,500 amperes

You might try contacting the people at the link below they produce an array of products for Corrosion control and Isolation up 100Kva if memory serves correctly.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources