replacing panel board interiors
replacing panel board interiors
(OP)
In cases of retrofits (grouted in panelboards, panel boards connected to many RGS conduits with seals etc.) , We have often specified replacing the interiors of old obsolete panel boards with new interiors and covers. The new interiors are much smaller than the old so clearance is not an issue. Some improvising is required to get the new covers aligned properly, however.
We have recently had a "paranoid" contractor refuse to do this work, as this is not a UL listed combination.
Is there a work-around to this issue based on clearances, original UL listing of panelboard can etc. The original equipment is probably thicker gauge steel than the new anyway. There is also more clearance than a new. So there has to be a systematic approach to legally validating what common sense says, i.e. no problem.
We have recently had a "paranoid" contractor refuse to do this work, as this is not a UL listed combination.
Is there a work-around to this issue based on clearances, original UL listing of panelboard can etc. The original equipment is probably thicker gauge steel than the new anyway. There is also more clearance than a new. So there has to be a systematic approach to legally validating what common sense says, i.e. no problem.






RE: replacing panel board interiors
RE: replacing panel board interiors
There are programs like http://www.ul.com/field/ which may also be offered by other NRTLs to individually inspect and so label the modified equipment with regard to appropriate UL standards. They could generate an exceptions report to show due diligence [but potentially acceptable compromise] on the part of engineering staff, facility owner and AHJ.
RE: replacing panel board interiors
RE: replacing panel board interiors
However, I'm under the strong impression that if you use a panelboard shop who is certified by the original panelboard manufacturer, that they can do about whatever they want to the panel and it will either maintain the original UL listing, or at least they'll provide a certificate for the panel which is just about as good.
I'd definitely recommend that you get a custom panelboard shop to do this work instead of your contractor.
Actually, I'm kind of surprised that your contractor has the morality and common sense to refuse this work -- to be honest, I've never met a contractor yet that would think twice about attacking a switchboard bus or frame with a drill and a sawzall to make a few little "enhancements" to the original design. Arguments about UL listings usually just make their eyes glaze over and they start mumblling things about engineers under their breath. . . .
RE: replacing panel board interiors
However, if it was, then your contractor is right: smaller equipment will mess up the Form compatmentation, for example if it was Form 4 - Type 7 (as in: you have to be an ... to get yourself electrocuted manipulating this one), the new version won't remain so. I know a silly frame can cost $2000 and that's why you'd like to keep it, so instead of the UL, have someone from the municipality or city hall approve the installation.
RE: replacing panel board interiors
Dick Waltermeyer
RE: replacing panel board interiors
So the bottom line is cehck with the local inspector and/or fire marshal who may accept a installtion which he deems safe within reasons ( the reverse is also true, he/she can reject a UL listed equipment as well, if deemed unsafe).