PT shielded cable close to capacitor banks

PT shielded cable close to capacitor banks

PT shielded cable close to capacitor banks

(OP)
Does anybody know a type of PT cable that has a shield that will minimize transients due to magnetic coupling?  This is for a sub with cap banks.  We tried using a 4 conductor cable with a copper shield but it turns out that doesn't reduce magnetic coupling very well.

RE: PT shielded cable close to capacitor banks

What about using sheilded twisted pair? The shielding needs to be ferrous to shield for magnetic field, I believe.

RE: PT shielded cable close to capacitor banks

Scottf is right on, you need ferrous shielding for magnetic circuits.

Maybe you could run your wiring in steel conduit.

RE: PT shielded cable close to capacitor banks


It may be worth investigating if indeed magnetically-coupled capacitor currents are introducing errors in the PT cabling.  {As implied, non-ferrous shielding is primarily effective for electrostatic influence.}  

If for instance, the PTs are used for capacitor-unbalance protection, some initial or quiescent voltage may be present from accepted capacitor-manufacturing tolerances, and somewhat influence what would be considered an otherwise near-zero secondary quantity, like on the order of a 0.05 per-unit value.  The need for sensitivity in ground-overvoltage relaying makes accurate determination of ‘neutral-shift’ voltage quantities important, and otherwise not “buried in the mud.”  [Reference IEEE Std C37.99-2000.]
  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources