Hi all!
CHWS for process aplication
What best way of an arrangement pipes of input
and output in buffer tank for obtain of gradual change temperature, at heat impact from loadings (at one level, one is higher than another, to arrange above, below, in middle)?
How to calculate its(tank) sizes?
Best Regards
CHWS for process aplication
What best way of an arrangement pipes of input
and output in buffer tank for obtain of gradual change temperature, at heat impact from loadings (at one level, one is higher than another, to arrange above, below, in middle)?
How to calculate its(tank) sizes?
Best Regards





RE: Buffer Tank
You may find your first question answered in a previous thread.
As a rule of thumb, you should have 8 liters of system volume for each kW of cooling.
I hope this helps.
RE: Buffer Tank
PS: I couldn't understand what a gradual change temperature is.
Regards,
Believe it or not : A Neutrino is so mass less(and electrically neutral) that, a conservative estimate states, it can pass through a 50 light year thick lead block.
RE: Buffer Tank
RE: Buffer Tank
The technological process works with sharp rises of temperatures.(10F/20s)
It's necessary to mix water so that:
1. Occurred initial heating of water practically immediately - for activation of chiller's loading system
2. The change from a minimum to a maximum must occured extended in time,and occured very smoothly. A time interval achievement of equality input and output temperatures will be proportional, I think, to the sizes a buffer tank.