sensor for control of cooling water temperature

sensor for control of cooling water temperature

sensor for control of cooling water temperature

(OP)
Does any one have a reference for the control of cooling water temperature (wet bulb/dry bulb temperature sensor).

If we use only the dry bulb temperature, we could loss some degrees but, is it really worth? During the summer, when we could need it, we have high humidity so it may be not relevant.

Kind regards

RE: sensor for control of cooling water temperature

I don't know what you mean by wet bulb temperature controller. If you have a temperature controller for cooling water at a minimum temperature required for your process or chillers, that would suffice your requirement.

Just on/off the fan based on chilled water temperature. You need not bother about air side temperature.

Regards,

Believe it or not : A Neutrino is so mass less(and electrically neutral) that, a conservative estimate states, it can pass through a 50 light year thick lead block.

RE: sensor for control of cooling water temperature

Are you refering to a dew point sensor?

You can use this type of sensor to control the operation of a chilled water control valve.

RE: sensor for control of cooling water temperature

Comparative Enthalpy Sensor. Inputs for economizer control based upon comparison of the enthalpies of the return and outdoor air streams.

RE: sensor for control of cooling water temperature

Enthalpy sensors.  High maintenance and pricey.
If the towers are controlled by vfd's or two speed controllers, provide a setpoint controller for the desired ecwt.  Otherwise a management system is required with some nifty algorithms.  I built one that provides fuzzy control of the setpoint that will change throughout the day.  We needed noise control at night, so we insured the towers were calculated oversized and ran about 4 gpm/ton of water through the chiller so that it would meet the minimum flow per cooling tower cell (water ran over 4 cells, design is 2 cell per chiller).

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources