water distribution
water distribution
(OP)
Are there any standards regarding the maximum water velocity that can be reached in water transmission /distribution lines for the following pipe materials:
1-Ductile iron cement lined
2- concrete pressure pipes
3- Steel pipes
1-Ductile iron cement lined
2- concrete pressure pipes
3- Steel pipes





RE: water distribution
In my experience, most water utilities limit normal flow to 5 ft/sec with exceptions for fire flow...
limiting factors are:
Friction loss: At speeds greater than 5 ft/sec the friction loss becomes large enough to change the hydraulic gradient such that steady pressures are not maintained or increased cost of pumping play a factor.
Water hammer: for every 1 ft/sec of speed, the pressure wave from a suddenly closed valve changes by about 50 psi. This occurs on both sides of the valve, upstream as a pressure increase, downstream as a pressure decrease. Up stream the pressure rating of the pipe may be exceeded, downstream the pressure can go into vacuum which may include column separation (cavitation), the vacuum conditions may induce backflow from services or leaks. column separation can destroy the lining of the pipe and anything else in the way. Steel and PVC pipe are less vulnerable because they deform to absorb some of the energy, but their pressure ratings are lower.
Lining removal: Destruction of the linings from long term erosion can occur with the water traveling at high speeds, many other factors are involved here, chemistry of the water, imperfections in the lining material ect.
Hydrae
RE: water distribution
the minimum allowable velocity in distribution system is 0.6 m/s
and general range accepted is 1.0-1.5 m/s
regards
RE: water distribution
As long as you can accomodate the resulting headlosses and surge pressures there is no other reason to limit max. velocity.
RE: water distribution