Tilt Panels out of Plumb
Tilt Panels out of Plumb
(OP)
I have a contractor who has placed panels up to 4 inches out of plumb. Panels are 26 feet high. Has anyone a reference to an acceptable out of plumb tolerence for panels?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: Tilt Panels out of Plumb
1 inch, maximum plumb variation over height of the structure or 100 ft, whichever is less.
at p. 230 in
Architectural Precast Concrete
2nd edition
pci Precast/Prestressed Concrete Institute
Chicago 1989