INTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS

Member Login

HANDLE


PASSWORD
Remember Me
Forgot Password?

Come Join Us!

  • Talk With Other Members
  • Be Notified Of Responses
    To Your Posts
  • Keyword Search
  • One-Click Access To Your
    Favorite Forums
  • Automated Signatures
    On Your Posts
  • Best Of All, It's Free!

E-mail*
Handle

Password
Verify P'word
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail.

Partner With Us!

"Best Of Breed" Forums Add Stickiness To Your Site
Partner Button
(Download This Button Today!)

Member Feedback

"...This was the ONLY place that I could find information that I could use to resolve the problem. So thanks once again to member TomSark and the SQL forum!..."

Geography

Where in the world do Eng-Tips members come from?
TBDaniel (Mechanical)
10 Oct 03 11:24
Is a there an IEEE code that regulates the materials used for mechanical fasteners connecting a copper busbar?  At this newly constructed power station we have experienced a short between two phases of the 4160 V busbar, which apparently initiated at a loose bolted connection on one phase.  The copper busbar is connected with what appears to be stainless steel bolts and nuts.  There is installed a flat washer on the bolt head end and a locking washer on the nut end.  Upon inspection, there were numerous bolted connections found loose, and numerous seized bolts.  Could there be a problem with a galvanic couple that removes metal from the washer and thereby loosens the joint?  Is there any torque criteria for these mechanical fasteners?   
peebee (Electrical)
10 Oct 03 12:12
Usually the manufacturer provides torquing data.  But if not, possibly UL 486?  I'm not personally familiar with 486 so I can't say for sure.

How old is the switchgear?  Has it been periodically maintained, including periodic torquing of all joints?  If not, have you at least done periodic thermal scans to identify loose joints?  You should be doing one or the other.

I doubt galvanic action is the culprit.  Copper and stainless should be pretty happy together.  More likely is thermal cycling.

rbulsara (Electrical)
10 Oct 03 17:05
See my Thread238-69135 for a similar question.

Normal practice is to use Grade 5 steel bolts with a flat washer on the hex side and a flat washer and locking washer and nut on the nut side.

As mentioned in other responses regular thermoscannig or retorquing(at least once a year) is a good way to track and find out any loose connections before they become a real problem.  NETA/ATS also lists the torquing values. Also switchgear manufacturers publish the data. You may also search the net.
busbar (Electrical)
10 Oct 03 17:41

Limited supporting information in NETA ATS ยง7.1.6

Specification info at
http://www.fciconnect.com//products/technical_01_01.asp
  
RAMConsult (Electrical)
10 Oct 03 19:39
Avoid the retorquing problem by using Belleville washers in the following order: bolt, belleville, flat washer, busbar, flat washer, belleville, nut.  The belleville washers have well defined compression/torquing values.
rbulsara (Electrical)
10 Oct 03 20:04
I beleive, for some reason belleville washers are not recommended for copper buses. Only good for aluminum. (or is it reverse?) Look up T&B catalog. (If get time in my office I will get some quote on this).

They have their issues.
busbar (Electrical)
10 Oct 03 20:28

FWIW, Key Bellevilles sells Phosphor-Bronze / Beryllium-Copper disc springs.
  
alehman (Electrical)
10 Oct 03 21:57
I think the problem with the poor connections was poor torquing (to little or too much) during assembly. That many connections don't just loosen up by themselves unless there is some extreme environmental condition. There should be a flat washer between the lockwasher and the bus.

Normally bellevilles are considered to be required only for connections involving aluminum conductors unless vibration is a concern. Many engineers specify them for copper also, but I don't believe it necessary unless vibration is a concern. Bellevilles are normally installed under the head of the bolt. The most common bolt material is zinc-plated grade 5 steel.

See Thread238-61717 for discussion of bolt torque and re-torquing. There seems to be no consensus.
jbartos (Electrical)
12 Oct 03 17:50
Suggestion: The busbar installations should be checked for stray currents and a need for cathodic protection.
jbartos (Electrical)
12 Oct 03 18:09
Suggestion: Visit
http://www.moeller.co.uk/documents/busbar_brochure.pdf
for low voltage busbar details
and References:
1. ANSI/UL 857 Safety Standard for Busways and Associated Fittings
2. NEMA BU-1 Busways
3. NEMA BU-1.1 General Instruction for Proper Handling, Installation, Operation, and Maintenance of Busway Rated 600Volts or Less
4. ANSI/IEEE Std C37.23 IEEE Standard for Metal-Enclosed Bus and Calculating Losses in Isolated-Phase Bus
5. Etc.

Start A New Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!

Promoting, selling, recruiting and student posting
are not allowed in the forums.
Posting Policies

LINK TO THIS FORUM!
(Add Stickiness To Your Site By Linking To This Professionally Managed Technical Forum)
TITLE: Electric Power & Transmission & Distribution Forum at Eng-Tips
URL: http://www.eng-tips.com/threadminder.cfm?pid=238
DESCRIPTION: Electric Power & Transmission & Distribution technical support forum and mutual help system for engineering professionals. Selling and recruiting forbidden.