Available fault current
So it happened again today when I gave an engineer an estimate of fault current at the terminals of a 120/240 V single phase transformer. He was agast. Dealt with lots of other utilities, and never heard of a 75kVA that could deliver so much current. First he had a hard time believing that half winding line to ground faults deliver about 1.5 X the full winding line to line value. He's going to check with some manufacturers on this point.
I assume infinite bus on the primary. I use a low limit impedance from our specs, not the nameplate, since transformer may be replaced at some point. I lower that value by a factor of 7.5% based on ANSI/IEEE impedance tolerances. Voltage is increased 5% also based on standards.
What's going on? Am I overly conservative? Why aren't others giving similar figures? On what basis are they ignoring the line to ground (most common type of fault)multiplier. What do you do?
RE: Available fault current
What about not having a perfect fault any way? There is always some fault impedance, usually ignored.
Do you have any numbers and examples of what your calculating? I did a job recently with a 75 kVA transformer (Z=1.5 %) and an AFC of 18 kA. That I didn't consider excessive since panels rated at 22kAIC are pretty common.
For a 75 kVA 120/240V single-phase transformer connected to an infinite bus on the primary, they estimate 22,331 A for a line-to-neutral fault at tranformer terminals.
Is that close to what you come up with?
I also used 1.5%. Full winding fault is 23.7KA. Half winding is 37.1kA. http://www.bussmann.com/apen/software/s_... says 20.8kA for the full winding fault. They evidently don't use the tolerances that I do and ignore the half winding fault. 18kA sounds pretty light. Did you include source or cable impedance?
I get a similar result if I use 2.3% instead 1.5% and back off the tolerances.
I like these old scanned documents. How relevant do you suppose this data is to the newer high efficiency low impedance designs.
For a 120/240V system, the impedance between the transformer and the service will limit fault current a bit.
The GE Pub referenced has been updated quite a few times over the years. I don't know if the data for distribution xfmrs has changed that much or not.
Isc= Full Amp/%Z
for 75 kvA, 240V L-L, 1.5% Z yeilds
(75*1000/240)/.015 =20,833A
For L-N fault only half the winding is involved and the kVA rating is also cut in half, %z remains the same. The L-N fault would come out half the L-L SCC. Am I missing something?
Yes you are. kVA doesn't matter directly, only voltage and actual impedance. We base the % impedance on the kVA, though, just to muddy things up.
My first thoughts were: half winding means half the voltage and half the impedance > it's the same. By this way of thinking all the impedance is in the secondary windings. The other extreme is to consider all the impedance in the primary. This impedance is reflected to the secondary by the square of the turns ratio. A line to ground fault links half the number of turns that the full winding fault does, so the reflected impedance is 1/4 of that for a line to line fault. Half voltage and quarter impedance means double the fault current. The real solution is to accuratly divy up the impedance amongst the windings. Test data doesn't provide this split, though. I used the Westinghouse method of estimating a multiplier by separating the r and x parts. In most cases, though, it comes out to about 1.5 times. One spreadsheet I downloaded someplace just uses 1.5.
I prefer to approximate using an infinite bus. Source impedances are small in relation to the transformer impedances in question. I'd also hate to have to explain to customers that the improvements we're continually making in the system might require them to rewire.
Yes, I agree.
I missed cutting the %z in half. Rated current remains the same, voltage is cut in half.
Other way of seeing this (which I should have done), half the voltage is required to flow the rated current through the half the shorted secondary winding, compared to the same requried to force the rated current through the full shorted secondary winding. This amounts to half the %Z.
jbartos,
///Agree.\\\
///There are also transmission line conductor impedances, beside the actual source impedance, meant to be large upstream transformer or generator.\\\
///Actually, the customers would like the smaller short circuit current levels since the infinite bus as the input for short circuit calculation tends to be very conservative. Obviously, if the power distribution is substantially improved, the short circuit currents would be increased. However, the Utilities are well prepared for those cases by using current limiting fuses.\\\
On the other hand does what i said (in my second post) make sense...I have to think this again.
Say 50V was required to circulate rated amp through a shorted 240V winding, same voltage will be required to circulate the rated current through half the winding as only half the voltage is induced in the secondary!
Volts per turn does not change!
Someone need to test this, as not much written literature is available. I still doubt more current at half the voltage.
Side note - low impedance / high efficiency 3-phase pad-mount transformers are also becomming common is smaller sizes (<225 kVA). Fault currents in these small systems are sometimes much higher than past experience.
If the two secondary windings were paralleled, then the impedance would be Z/2 + Z/8 = Z·5/8. Current would be 120/(Z·5/8) = 16667A, 80% of the 240 volt fault.
The impedance changes for the half winding fault. Different turns ratio means you've cut that impedance assigned to the primary and transfered to secondary to 1/4 (turns ratio squared) the value if would be for a full winding fault. In your example, half winding fault impedance is (1/2)*0.5^2+1/4 =0.375X that of the full winding fault. With half the voltage, current is 1.333X. An easier way might be to do the calculation on the primary side for each case, then transfer the result across the turns ratio of the transformer for each case.
I agree, there is not much written. The GE pdf that DPC suggested does touch on it. They claimed it could be up to 2X. They also touch on the r and x factors that Westinghouse uses. The Westinghouse reference is the old green "Distribution Systems" book. See pages 222 and 223. They don't relate it directly to fault current. The ZH1-2 value they are calculating is theoretically what one would measure on the primary with X1 and X2 shorted, so it is applicable to fault calcs.
Guess I'm right, the half winding multiplier is being ignored. Even jghrist is unaware.
Alas, I haven't had access to the old green Westinghouse distribution systems book for many years. When I did, it was very dated but contained a lot of things not available elsewhere.
It would be interesting to do an impedance voltage test on a distribution transformer with X1 and X2 shorted. Also with the two windings in parallel. Seems that you would need this for a bank of single phase transformers serving a 120/208 load.
contains another fault current calculator that simply uses a 1.5X multiplier. Still doubtful rbulsara and alehman? I was too at one time.
jghrist,
You had to point that out about the parallel windings didn't you? Back to my spreadsheet.
I am still not convinced. While I am not saying you are right or wrong. I am also trying to reason. I am surprised if this was such a big deal, it would have been well documented somewhere in so called standard tables that are available for all kinds of transformers and SCC they can provide. Utiltiy companies would have made big deal about it and all residential panelboards would have to be 42kAIC rated minimum and which is not the case. 10kA rated would almost become a no-no.
I would like some tests. Increase in current may be due to considering the parallel windings. I know one of the persons who is involved in developement of EDR and will check out.
For one thing, if you look at the equivalent circuit of a transformer, (See Std. Elect. Engineer's Hand Book) the reactance of the transformer in ohms is a fixed value X, a result of mutual and leakage flux. The reactance of a tranformer is NOT Xs+Xp , adjusted to turn ratios. The nameplate %Z is a test result value and not a straight inductance measurement. Only conversion to turn ratio apply to Rs and Rp and load impedance Z which is zero for our discussion.
When half the winding is linked, I would think the mutual leakage flux would be half? Some one need to verify this.
If it is so, %X remains the same. You can play around with values of R which is not a overriding factor at all.
I am not in my office, if i get sometime I will have some manufacturer test this for us.
Also a per unit value is the same for either voltage. For a minute neglect the R.
For 75kvA,240V xfmr, the base Z = 240V/312.5A. And for 1.5% per unit reactance, hte ohmic value will 0.01152ohms .
For the half winding, the base Z = 120V/312.5A. If the half the linkage were to cut the mutual reactance in half, it will be half of .01152 ohm and the per unit value will be (.01152*0.5)/(120/312.5)=.015 or 1.5%, the same per unit value.
It is in some, as DPC pointed out, and ignored in others. And all the tables are too old. The line to ground value drops quickly with cable length, and at some point the line to line will exceed it. Maybe they all assume cable length is sufficient.
"Utiltiy companies would have made big deal about it"
Seems my colleagues are ignorant of the effect.
"For one thing, if you look at the equivalent circuit of a transformer, (See Std. Elect. Engineer's Hand Book) the reactance of the transformer in ohms is a fixed value X, a result of mutual and leakage flux. The reactance of a tranformer is NOT Xs+Xp , adjusted to turn ratios. The nameplate %Z is a test result value and not a straight inductance measurement. Only conversion to turn ratio apply to Rs and Rp and load impedance Z which is zero for our discussion."
Any impedance whether real or reactive must be adjusted by the square of the turns ratio in order to find its equivalent value when viewed from the other side of the transformer. I don't have the standard handbook handy, but be aware of any equivalent circuit. They are all approximations to some degree or other. The equivalent circuit that lumps all the impedance on one side or the other is not applicable here. The one to use has an ideal transformer in the center, which indicates where to apply the N^2 adjustment.
The fact that his name can be truncated to form my moniker is pure coincidence.
This is a table pulished by Arizona power service, upto date for 2003.
Includes infinite bus and 20 feet of cable (a very reasonable assumption), also seem know that L-N and L-L could be different for single phase xfmrs. Yet, for 100kvA,240/120V max. Isc (equipment rating ) is 22,000A.
I cant see 37,000A for a 75 kvA tx even with 20 feet of cable rated for 80% of service size. Of course exact cable size or impedance is not given, but still indicative of the fact that no need to exaggrate our estimates.
I think that if you use the minimum allowable impedance according your specs, you are conservative enough. IEEE Std 242 (thanks Borti) doesn't have a plain 1.5 fault current multiplier, however. There is a multiplier for the transformer resistance (0.75) and a separate one for reactance (0.6 for 75 kVA). The effective multiplier for fault current depends on the X/R ratio of the transformer.
If X/R is 1.8 as suggested in IEEE-242, then the fault current multiplier would be 1.566 not 1.5. Any X/R > 1.182 would give a fault current multiplier > 1.5.
As you say, the line-to-ground fault current drops off considerably with service cable length. Including some minimum cable length in the calculation would be reasonable.
I'm still curious about the effect of paralleled windings. Surely, the available fault would be higher for paralleled windings than for a single winding.
x1=1.6*pi3*f*N12*r/L*((1-p)*d3+d1/3)
x2=1.6*pi3*f*N22*r/L*(p*d3+d2/3)
xeq(ref to winding 2) = x1*(N2/N1)2+x2
N= # of turns
r= mean radius of winding
L= length of winding
p= fraction of flux linking inner winding only
d3= space between windings
d2= depth of inner winding
d1= depth of outer winding
Without knowning the configuration of the secondary winding, it would be impossible to calculate the equivelant leakage reactance while utilizing half of the winding. Short of measurement, manfuacturers pubished data is the only way to go.
"If X/R is 1.8 as suggested in IEEE-242, then the fault current multiplier would be 1.566 not 1.5."
Exactly how I do it in my spreadsheet with various multipliers based on the X/R value of each size transformer. I said "about 1.5X" above. Still bothers me I'm using old data for new transformers. The IEEE committee dropped this whole section for the updated standard, so maybe they were unsure of its applicability also.
"I'm still curious about the effect of paralleled windings. Surely, the available fault would be higher for paralleled windings than for a single winding."
Going by the Westinghouse diagram, if I parallel and short the secondary windings, I get an impedance of ZHX13 looking into the high side. This is simply the percent Z refered to the high side. Same high side current, twice the low side current as for the full winding.
Trouble is, if I try the same thing with windings in series, I don't get the same impedance. I thought this was how ZH13 was defined, but a ZH12 term remains. Still missing something here, or else the Westinghouse diagram is wrong.