water hammer in down stream of F & T steam trap of heater
i am facing a problem of knocking in down stream of float & thermostatic trap intermittently even heat load is more or less remains steady. what can be the probable reasons?. we have measured the pressure down & up stream of trap. as per the design of trap it is ok. chest pressure of heat exchanger is more than ( sufficient based on pressure drop calculation for condensate flow) the condensate header pressure.
RE: water hammer in down stream of F & T steam trap of heater
A rule of thumb is to have the vapor velocity in the condensate header < 50 ft/s. If it is too fast, the liquid in the bottom of the line can be picked up in waves and convert to plug flow. This will cause waterhammer at elbows, valves, or reducers. Even with a very small mass percentage of the condensate flashing to vapor, the vapor will occupy nearly all of the volume. Also, it is best to minimize vertical rises in the condensate line.
Another item that you may consider is vertical drop from the heater. If there is no vertical condensate collector, you could get blow through when the trap opens.