our local standard requires neutral wire colour code to be white.can somebody tell me if i have to follow this for the neutral of CT's and PT's used for metering and protection.
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
CT & PT Insulation colour
|
CT & PT Insulation colourCT & PT Insulation colour(OP)
our local standard requires neutral wire colour code to be white.can somebody tell me if i have to follow this for the neutral of CT's and PT's used for metering and protection.
Red Flag SubmittedThank you for helping keep Eng-Tips Forums free from inappropriate posts. Reply To This ThreadPosting in the Eng-Tips forums is a member-only feature.Click Here to join Eng-Tips and talk with other members! |
ResourcesWhat is rapid injection molding? For engineers working with tight product design timelines, rapid injection molding can be a critical tool for prototyping and testing functional models. Download Now
The world has changed considerably since the 1980s, when CAD first started displacing drafting tables. Download Now
Prototyping has always been a critical part of product development. Download Now
As the cloud is increasingly adopted for product development, questions remain as to just how cloud software tools compare to on-premise solutions. Download Now
|
RE: CT & PT Insulation colour
Usually, though, control wiring (such as PT & CT wiring) can be whatever color you please.
Might wanna check with your local authority.
RE: CT & PT Insulation colour
In both cases the wire sounds like it is used as a grounded-circuit conductor, and color could conceivably be enforced under that aspect.
RE: CT & PT Insulation colour
RE: CT & PT Insulation colour
Same for busbar.
RE: CT & PT Insulation colour
RE: CT & PT Insulation colour
Assumptions:
1. Your neutral is grounded.
2. This is field-installed wiring, routed outside of a switchboard. This is not factory-installed wiring, and it's not all contained within a switchboard. You're routing from a CT cabinet or similar, via conduit or similar, to some remote devices.
3. This is considered Class 1 control wiring per NEC 725.
That said, I can't find anything in the NEC that would permit you're neutral to be any color but white or gray (grey?). . . . except possibly NEC 725.25 Exception No. 1. And even then, I think it could possibly be interpreted either way . . . . Unfortunately, I've always found 725 to be a very difficult article to read/understand/apply.
Your best bet is probably to call up your local inspector or plan reviewer, and see what he thinks.
Has this already been installed? Do you have any good reason to make it some color other than white or gray?
Also, please note that if this is factory-installed wiring located in a switchboard, then most likely the wiring is type SIS, which is ALWAYS gray in color, and factory wiring does not fall under the scope of the NEC.
Hope this vague answer helps.
And "wahala-wasahala", or however you say "welcome" in Saudi Arabia (that one phrase constitutes my entire Arabic vocabulary).
RE: CT & PT Insulation colour
One comment — NEMA Std ICS1-2000 for Industrial Control Panels §7.6 states “…white indicates the grounded neutral conductor or the circuit.” I understand that to mean that for internal wiring, white as grounded-circuit conductor is acceptable but not mandatory.
RE: CT & PT Insulation colour
i have a control gear with motor starters using 239 multilin relays .the secondary of the phase ct's used have x1 & x2. x1 is the ungrounded circuit conductor and x2 is the grounded circuit conductor. the color coding used for the x1 is white and for x2 is black. the inspector was arguing that the color be reversed,as the local std says all neutral should be white. we told him that nec or the local stds does not state the conductors used for cts and pts be considered for the color coding. but of no use!!! can you help to support our argument. by the way
Ahlan wa Sahlan - Arabic for welcome
RE: CT & PT Insulation colour
RE: CT & PT Insulation colour
Doing things completely opposite of a recognized practice may be troublesome during operation/debugging/troubleshooting.
RE: CT & PT Insulation colour
1. Route the conductor through the CT the other direction (change all of them) and reverse your X1 X2 connections OR
2. Just reverse the connections. Verify with 239 literature that this is not going to screw up the power readings (PF), solution #1 above should not mess with any functionality or measuring of the 239.
You have to work with your inspector, if this is the way he wants it then make it that way in order to keep relations good because, at least in the US, he can make life hard for you.
RE: CT & PT Insulation colour
What do you do for 3ø wye connected CTs and VTs? If the NEC wire colors are deemed to be required for CT and VT cables, how do you use standard ICEA control cable color codes? Method 3 Table K-2 4/c cable has Black, Red, Blue, Orange. No White for grounded conductor. Method 1 Table K-1 has Black, White, Red, Green. To use White for the grounded conductor, you would have to use Green as a phase conductor. What I have done is to use the Green as the grounded conductor if using Table K-1 and use Blue, tagged as Green if using Table K-2.
RE: CT & PT Insulation colour
The ICEA “K2” colors and recoding scheme seems to have been addressed in 99NEC200-6(e) Ex. 1: Where the conditions of maintenance and supervision… grounded conductors in multiconductor cables identified at their terminations at the time of installation…
RE: CT & PT Insulation colour
Label all wires as they appear on the shecmatic ( online, synchronizing diagram etc) with permenant slip on wire sleeves. IF you designing the system prefix the wires with a "CT" or "PT". If you didn't design the equipmentm then tag tag the conductors some way during commissioning.
I like to specift that CT circuit conductors a larger size (#10 over here where we say color). The larger wire may not be necessary but the size make it identifable.