115 kV Substation Switching Scheme

115 kV Substation Switching Scheme

115 kV Substation Switching Scheme

(OP)
I work for a private generator that wants to interconnect with the local utility grid.  I'm proposing to open an existing 115 kV transmission line (in and out) and interconnect the generator step-up transformer with a 3-breaker ring bus.  Is there a better substation switching scheme to use (cost, reliability, etc.)?  Any information would be greatly appreciated.  Thanks.

rrivas

RE: 115 kV Substation Switching Scheme


The scheme you are proposing is a good one. There is a lower cost scheme, which is to provide one breaker only at the tap location, which will disconnect your generation from the 115 kv line. The disadvantage of this scheme is that your generation will be tripped for a fault on either section of the 115 kv line. This may or may not be acceptable to you, depending on the length of the line, its outage record etc.

RE: 115 kV Substation Switching Scheme

The ring bus is a good workable solution.  It will be expensive at 115 kV and require some land.  Utility may want something more elaborate, but ring bus should be more than adequate.  

RE: 115 kV Substation Switching Scheme


In ANSI regions, standards to thumb through might be…

C37.113-1999 …Protective Relay Applications to Transmission Lines
C37.95-2002 …Protective Relaying of Utility-Consumer Interconnections
C37.91-2000 …Protective Relay Applications to Power Transformers
C37.102-1995 …AC Generator Protection
C37.101-1993 …Generator Ground Protection

The design needs to be coordinated with the line owner, his protection scheme and possibly varied operational modes.  
  

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources