Minimum Reinforcing of Pedastal

Minimum Reinforcing of Pedastal

Minimum Reinforcing of Pedastal

(OP)
This is a waste of time to me but I have to resolve this question forced upon me by a Contractor's interpretation of ACI 318.

This concerns 46 inch square "pedastals" for a six legged water tank structure.

My interpretation: Use ACI 318 -10.8.4 and 10.9.1 for compression members and you get a minimum reinforcing ratio of 0.005.

or use ACI 318 - 15.8.2.1 for pedastals and you get a minimum reinforcing ratio of 0.005.

END OF STORY.

Contractor says you look at 15.8.2.1 and get 0.005Ag, "then" you go to 10.8.4 and divide by two to get a minimum reinforcing ratio of 0.005Ag/2!

THEN I GET THE COMMENT that ties are NOT required for pedastals!

Is there any validity to Mr. Contractor's theory.  Thanks.

RE: Minimum Reinforcing of Pedastal

You are correct.  15.8.2.1 specifies the minimum amount of reinforcing that must cross the interface between a pedestal or column and the footing.  This is NOT the minimum longitudinal reinforcing ratio in the pedestal or column itself.

RE: Minimum Reinforcing of Pedastal

Mr. Contractor may push for no ties but if you ask him to sign a nifty letter saying he takes full responsibility should the pedestal crack or fail - let's see what he does.

RE: Minimum Reinforcing of Pedastal

Who is the Engineer of Record, You or Mr. Contractor?

RE: Minimum Reinforcing of Pedastal

RMPE,
  First of all, if your pedestal satisfy the aspect ratio in Chapter 15, then theoretically, you do not need any reinf. for 'plain concrete' structure.  However, it is always a good practice to provide minimal reinf., i.e. 0.005Ag for structural integrity and premature shear cracking in plain concrete due to accidental bending or impact during construction

RE: Minimum Reinforcing of Pedastal

(OP)
Obviously, it wouldn't be prudent to build a 200,000 gallon water tank on unreinforced pedastals in my opinion!

On the other hand, I do not see where it says "pedastals" have to be reinforced at all, only 0.005Ag across the "interface between pedastal and footing".

ACI said use the 0.005Ag.

Thanks for the comments

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources