We have several artesian or "flow wells" at our site. There are Druck pressure transmitters in the wells at 35 feet. The problem we are having is programming our SLC505's to adjust for the natural variations of the static pressure which can range from 2psi in the winter to 12psi in the summer. 1psi = 2.31 ft. of water. You can see my delema. Does anyone have experience in this matter? Any help would be appreciated. Thanks in advance. Dixie
We have several artesian or "flow wells" at our site. There are Druck pressure transmitters in the wells at 35 feet. The problem we are having is programming our SLC505's to adjust for the natural variations of the static pressure which can range from 2psi in the winter to 12psi in the summer. 1psi = 2.31 ft. of water. You can see my delema. Does anyone have experience in this matter? Any help would be appreciated. Thanks in advance. Dixie





RE: Drawdown of artesian well
If you want to know the water level, the pressure is a direct relationship. More info please.
RE: Drawdown of artesian well
What you need is a dynamic reference level to measure the difference or draw down value. One way to get this is to use a level reading from a well nearby that is not in use. Your SCADA system can then subtract this value from the operational wells and the result is the "drawdown".