15kva DELTA to WYE tranformer loading

15kva DELTA to WYE tranformer loading

15kva DELTA to WYE tranformer loading

(OP)
I am in process of designing a machine that requires a 15kVA transformer to accommodate international voltages.
INPUT:  DELTA 380/400/415/480 L1-L2-L3, Earth
OUTPUT: 208 L1-L2-L3-N (N bonded to Earth)
The balanced loads will be a 6kw heater (30% duty cycle) and a 1hp blower. The remaining loads are all single phase. I plan to balance the loads as best as possible across the 3 phases.
I can hook up a majority (but not all) of the loads L-L (208 across 2 phases) or L-N (120 single phase) since they are universal voltage switching power supplies. Does anyone see a problem with placing the loads L-L rather than L-N? Especially a problem with the transformer – circulating currents, neutral issues, etc.?
Thanks, wwilson

RE: 15kva DELTA to WYE tranformer loading

If your power supplies have standard 120-volt receptacles, I would STRONGLY recommend you wire them at 120 volts, or change the plug or plug & cord out for use at 208 volts.  That's the only problem I'd foresee with going L-L.

Beyond that, L-L will probably help with load balancing, but will require 2-pole breakers rather than single-pole breakers be used for each load.  L-L may permit you to use slightly smaller wire than with L-N.

I don't see where L-L vs. L-N would have any impact on either circulating currents or neutral issues given the loads you've described, as there's nothing there that sounds like a high-harmonic load.

RE: 15kva DELTA to WYE tranformer loading

Suggestion to the original posting: L-L single phase loads will need twin-breakers for the circuit protection, which is somewhat more cumbersome than L-N single phase circuit loads protected by single pole circuit breakers. Also, some L-L loads are not permitted, e.g. fluorescent fixtures in some jurisdictions. The benefit of L-L circuits and loads is in smaller wire gage and potentially smaller physical sizes of the loads.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.