screw comp. with 77 centig. oil temp
i have new screw compressor ref. system with:
77 centig oil.temp
55 centig ambiant.temp
19.8 bar discharg.P
4.8 bar suction.P
40.5 centig suct.T
67.0 centig disc.T
15.0 centig evap.T
100 % (capacity)
SAB 83 (SABROE(YORK)COMPRESSOR)
DO YOU THING THE OIL TEMP. IS A NORMAL VALUE?WHY?
77 centig oil.temp
19.8 bar discharg.P
4.8 bar suction.P
40.5 centig suct.T
67.0 centig disc.T
15.0 centig evap.T
100 % (capacity)
RE: screw comp. with 77 centig. oil temp
I would consider the oil temperature too high.
Have you consulted the Manufacturer about the temperature?
Does your compressor have oil cooler
Providing this is an ordinary oil injected compressor, if the Oil in the separator or sump gets colder than the condensing temperature you will have a tendency to draw refrigerant to the oil reservoir...there always needs to be a difference between them or the refrigerant will disrupt the lubricant film when the mixture is exposed to a hot surface, which is in effect all the internal wetted surfaces of a screw compressor and the bearings as well.
So the package needs an oil temp higher than 67 C. There may be means to get it under 77, but not by all that much.
What is the nature of the application that all the temps are so high?