what  ia the best way to test xlpe cables? DC or Ac

RE: xlpe cables

Most cable manufacturers reccomend against hi-pot DC testing of XLPE cables, and suggest an AC test instead (effectively a no-load energization test).  I would reccomend an insulation resistance test prior to energization though, just to pick up possible "gross" faults.

RE: xlpe cables

DC hipot testing of XLPE cable is considered possibly detrimental if the cable is has been in service in a moist environment for more than a year or two.

DC field test for medium-voltage cables: why can no one agree?
Mercier, C.D.; Ticker, S.; Industry Applications, IEEE Transactions on, Vol.34, Iss.6, Nov/Dec 1998

Recommendations in HV DC testing of MV cable insulation
Finke, B.H.; Industry Applications Magazine, IEEE, Vol.3, Iss.5, Sep/Oct 1997

RE: xlpe cables

Either AC or DC Hipot testing, which are destructive tests when the test voltage is above the rating of the cable, is recommended usually for Acceptance Testing(new cable) only. These type of tests will prove that the cable has no insulation and splice/stress cone problems.

Maintenance Testing on cable in service is a different story.
For years, hipot(DC or AC) was recommended at a test voltage and time significantly less than the Acceptance Test voltage(but still above the cable rating), but frequent sudden cable failure during the test(to a cable, I might add, that usually had no spare and no plan for immediate replacement), leaving the plant down with sdome very unhappy customers, has led quite a few people to recommend other, non-destructive tests, such as Polarization Index, lower-voltage Hipot, Doble Power Factor, Partial Discharge, etc.

It is important to note that AC or DC voltage doesn't matter as much as the test voltage level. AC test voltage recommendations are usually less than DC values for the same cable rating, since rms AC has peak voltages about equal to the DC test voltage levels.
Also, DC tests can be conducted with a small test set, while AC tests for a long cable sometimes may require a test set that must be transported by something close to your typical 18-wheeler.

RE: xlpe cables

Very low frequency AC is an alternative that is considered by some to eliminate the long-term detrminetal effects of a DC hi-pot test while using a reasonable sized test test.

RE: xlpe cables


Guide for Field Testing and Evaluation of the Insulation of Shielded Power Cable Systems IEEE Std 400-2001 is one overview—discusses merits of DC, power-frequency and VLF overpotential testing of cables.

Paul Gill’s Electrical Power Equipment Maintenance and Testing is another source.
  

RE: xlpe cables

I believe ERA Technology in the UK do, or did, offer very low frequency testing of power cables as one of their services, as suggested by Alehman.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources