hi,
does any experience this problem before :
On the BMS/BAS monitor screen, the chiller tonnage is X ton. but when i used the formulea
ton= (16*flow(l/s)*Delta T)/24, the value is often different ?
This is due to equipment calibration out. I yet to ask my BMS guy wat wrong ?
Is there a standard algorithm for chiller sequencing using the tonnage.
 

RE: BMS reading for chiller

Your equation will be correct if the temperature difference is in °F, not °C. If in °C you have to factor by 9/5. You must use the GPM & temperature sensed by the BMS.

RE: BMS reading for chiller

Hi bundy!
1. The real chiller's capacity can vary depending on loading.
2. Try to use the following formula:
  TR = Flow(l/s) x Evap.Range(deg C) x 4.187 x 0.2844

RE: BMS reading for chiller

(OP)
hi sifox,

just need to clarify something, what does Evap.range stand for ? evap refigerant temp ?

thanks.

RE: BMS reading for chiller

Diff. between chilled water inlet and outlet temperatures.

RE: BMS reading for chiller

Bundy's formula x 9/5 should equal Silfox but Silfox should review the constants because the product should be = (16x9)/(24x5)

RE: BMS reading for chiller

Q = m x Cp x Delta T

Capacity in Btu/hr = Flow in GPM x 500 x Delta T in °F

RE: BMS reading for chiller

SilFox's formula is correct.

Heat removed Q(kJ/sec) = m(kg/sec) x Cp(kJ/Kg0C)xdT(0C)

1 kg water occupies about 1 liter volume

so Q (kJ/sec) = flow(l/s) x 4.18(kJ/Kg0C)xdT(0C

1 Ton = 3.517kJ/sec

therefore Q(ton) = (flow(l/s) x 4.18(kJ/Kg0C)xdT(0C)/3.517
= (flow(l/s) x 4.18(kJ/Kg0C)xdT(0C)x0.2843

Regards,

RE: BMS reading for chiller

We are chasing decimals. All the above formulas are correct when rounded off, providing the correct units are used as noted above.

I am used to using Tons = GPM x 500 x (°F TD)

RE: BMS reading for chiller

Correction Tons = GPM x 500 x (°F TD) / 12000

RE: BMS reading for chiller

Is the BMS guy using flow and dT to calculate tonnage? He might be using the chiller load value off the chiller panel. Just a thought.

RE: BMS reading for chiller

If the system is sophisticated enough to have a BACnet interface with the chiller, the chiller will provide for a tonnage variable from the chiller panel.  If you are observing the remote temperature and flow meter sensors in your EMCS, that calculation will be based on the EMCS sensors and you are comparing that to the chiller.
The chiller is reading a completely different pair of sensors than your EMCS mounted sensors.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources