Current Unbalance Relay
I'm sourcing for a current unbalance
relay for capacitor bank protection.
It's a 3-phase relay and input 5A.
It has to be single function relay and
inexpensive.
If you guys have any recommendation
on manufacturers, pls let me know.
Thanks a lot.
TK
RE: Current Unbalance Relay
You may want to review IEEE Std C37.99 …Protection of Shunt Capacitor Banks
Suggestion: Reference:
IEEE Std 242-2001
 CHAPTER 6
6.4.2.4 Capacitor protection
 CHAPTER 12
12.5.5.2 Unbalanced current protection
Normally, individual capacitors may be protected by fuses.
ABB has SPAJ 160C which is specially designed for capacitor bank protection .it has many more functions available than mere unbalance potection.