What are the 3 phase voltages in the USA ?
We have to install UV dryers in the U.S.A.
In Europe, 3 phase + ground (Y) is common in industrial sites. Phase to phase around 400 VAC, ground to phase 230 VAC.
What is common in the U.S.A. One hears, 480 VAC delta, no ground.
Is there a standard ?
RE: What are the 3 phase voltages in the USA ?
Most common in the USA is 480Y/277 , 3phase, 4 wire grounded system for equipment in commercial and industrial sytems. Commercial lighting normally is 277V.
Convenience outlets, whether residential, commercial or industrial are always 120V, a part of 208Y/120V, Y system. Therefore, a system of step-down transformers , 480V delta to 208Y/120V is always present in commercial and industrial systems.
As with any other place, exceptions are always present which include ungroundned or groudned delta systems. Always check with your clients.
And for your further informatin:
Resiential systems are normally fed by 2 phases and a neutral (single phase, 3 wire) which in fact is part of a 208Y/120V , Y grounded system. 480/277 is never used in the residential systems.
Many older residential systems would have 240/120V, single phase 3 wire systems.
Hope this helps you cause.
Grounded 480Y/277 is standard for larger commercial and industrial applications, however many small commercial services (esp. retail) are 240/120 single phase 3 wire or 208Y/120 3 phase, 4 wire.
Some industrial installations use 480Y, with high-resistance grounding. Ungrounded 480 is very rare except in a few old industrial applications. Many old industrial systems are 240V 3-phase delta, either ungrounded or with B phase grounded.
If you need something “chiseled in stone” about US voltages, search for ARI Standard 110-2002. Last time I checked, it was free, whereas the official document is ANSI Standard C84.1-1995 that costs $30. For low voltage, they seem identical with one exception. For specific regions, electric utilities generally publish availability in their online “service conditions.” {There are no small number of electric utilities on the North American continent.} For typical industrial-machinery branch and feeder circuits, don’t count on a neutral conductor routinely carried with phase conductors.
120V control power is usually derived from a machine-tool control power transformer served from fused [208-600V] line conductors served to equipment. Where 230V control may be tapped from a 400Y 4-wire circuit, a similar 277V prectice is rare.
Most common is Phase to phase nominal of 480 VAC, ground to phase 277 VAC.
For smaller systems, Phase to phase 208 VAC, ground to phase 120 VAC.
For larger systems, Phase to phase 4160 VAC, ground to phase 2400 VAC. (probably resistance grounded neutral at this level).
(For larger systems, Phase to phase 13800 VAC, and so on).
The best method is to refer the correct standard to get full information. ANSI C84.1-1995 indicates full details of voltage systems for 60 Hz (US & Canada) and also describes useful definitions for LV systems.
Regards!
Kiribanda
For specific application and available site voltage consult with the local utility company regarding interconnection for the intended motor load. Typical requirement are described in the enclose site.
http://www.duquesnelight.com/connections/esir16.htm
http://www.duquesnelight.com/connections/esir15.htm
http://www.duquesnelight.com/connections/esir36.htm
Lyledunn
For instance, I do not know how will be possible to change from 60 Hz to 50 Hz in the US. Other example is to change in the US typical residential voltage from 110 V to 220V as many other countries in Europe.
There are issues such as NEC compliances, construction regulation and building codes requirement, insurance polices, testing, UL certification, engineering standards, safaty practice, etc. that also require to be changed.
There is a tremendous variety of electrical services in the U.S. Here is a short list of some of the more unusual electrical services <1000 volts that I have personally encountered in the last few years:
240-volt 2-wire with end ground
277-volt 2-wire with end ground
480-volt 2-wire with end ground
240/120-volt 3-wire 1 phase with end ground
480/240-volt 3-wire 1 phase with end ground
416/240-volt 4-wire wye with grounded neutral
416/240-volt 4-wire wye with ungrounded neutral
416/240-volt 4-wire wye with grounded phase
480/277-volt 4-wire wye with grounded phase
480/240-volt 6-wire delta with one center tap grounded
480/240-volt 5-wire delta with one center tap grounded
480/240-volt 6-wire delta with one corner grounded
830/480-volt 4-wire wye with grounded neutral
120-volt 3-wire grounded delta
120-volt 3-wire ungrounded delta
///Europe has somewhat stricter the power distribution system voltages with fewer deviations than USA.\\\
///This is very old system, nowadays replaced by 480/277VAC grounded wye in most cases. The ungrounded 480V or similar system voltages are used for dedicated loads, only. The ungrounded system voltages experience detrimental transient overvoltages due to arcing.\\\
My point is it would cost way to much money for everybody to convert to usa standards and vise vera. I like the idea of standardization if it doesn't cost me any money, let the other guy pay for it, but that will not happen.
Europe is faced with a similar problem now that the nominal voltage is 230V. The tolerances on this nominal voltage have been widened, at least for the medium-term future, so that the UK with 240V and the rest of Europe with 220V don't have to replace much of their distribution infrastructure to comply. The cost of such wholesale replacement of equipment would, as you say, cost way too much.
Standardization? Ask every industry / commercial building / residence to rewire to a new voltage? Not on, I'd guess, except maybe a 50 yr+ dual standard strategy. I must say, though, those British 240V "ring mains" sure have a lot of advantages for install cost.