Wood Truss Load Responsibility
I'm providing some engineering consulting services on a structural failure of an agricultural building where the roof collapsed under snow loading. The roof was comprised of wood trusses spaced at 4'-0" o.c. and spanning about 75 feet. I analyzed the trusses, using the truss manufacturer's spec sheets for capacities, and found pretty quickly that they failed due to an unbalanced snow loading on the leeward side of the roof. That's not really the issue.
Most wood trusses are called out by the designer of a project. This is usually an engineer. But in this case, there was no engineer. The "farmer" was coordinating the activities of the work, called up a local lumber yard and ordered the trusses. The lumber yard conveyed the order to a truss manufacturer who simply plugged in 20 psf for the roof snow load and sent the underdesigned trusses on their way.
The Truss Plate Institutue Specs and all other info I can gather dictates that the designer is responsible for calling out or determining the proper live loads. But in this case, the farmer didn't have the background/know-how to do so. He had no idea what a snow load even was. The truss designer knew that these trusses were headed to a ground snow load area of 45 psf.
Wouldn't it be the Truss designer's responsibility to at least question his own decision to use 20 psf?
RE: Wood Truss Load Responsibility
TrussEngineering.com
Have a full article regarding truss design responsibilites.
Did the building require a building permit? Due to size or span, etc? If it did, why wasn't one obtained? Did the building inspector know that construction was ongoing?
Was a contractor involved? He may have known something about permits? loading, etc? Was the loading used common for the area? Most truss suppliers, here will querie a loading if they don't think it's correct.
Why did the owner not get permit or professional help? ignorance or to save money?
Were shop drawings (even 8-1/2x11) prepared by the truss supplier? Often the shop drawings have a note regarding spans greater than 60' requiring an engineer. Are there any attached or referenced notes to the shop drawings? Did the shop drawings or transmittal require approval of the loading? Most truss suppliers' software accommodates unbalanced loading, reduced loadings (for ag buildings, etc.), slippery roofs...
Did the truss actually fail due to load? The 4' span would indicate purlins (truss supplier's name for even 1x4's @ 16 on the flat) and metal roofing. Was a 'slippery' roof considered in the analysis? Was the weight of snow actually determined? or had there just been a lot of snow? I use a 4" dia. piece of septic system pipe, with a sharpened and serrated end to obtain snow cores for weighing.
How did the owner install the trusses? were they damaged in the process of installation? 75' span trusses are something not normally handled by forklifts.
Did you take a look at the horizontal bracing system. Many of the failures I've seen are due to incorrect horizontal bracing or damage during installation.
Truss fabricators prefer to be responsible for what they do best... make trusses. The drawings can specify that they be responsible for lateral loading, etc.; basically everything above the top plate. Is there any correspondence from the owner to the truss supplier to the effect that he was doing this himself? or did the owner simply order trusses, say, from a lumberyard, to span 75'?
I've got to run... and will add to this, later.
Dik
This can be a classic example of the great big loop hole between the UBC and the TPI code. The UBC refers the designer to the TPI which in turn says that the engineer of record is responsible for the web bracing. Usually the truss company's calcs will indicate which webs must be braced and where. Then the design engineer has to find the compressive force in these webs and determine how the keep the web from buckling. This can either be 2x4's connecting the webs to a hard point or adding another member to each web to reduce the L/D. The point is that many designer's don't know about this requirement and neither do many building departments, or it they do, they don't enforce it.
In this case, there wasn't an engineer - so the web bracing could have been neglected or the builder could have just guessed at the bracing.
I would have liked to seen some sort of warning or notice in Section 2321 of the UBC. Reviewing Section 2303.4.1, item 17 of the 2000 IBC actually addresses the problem, but how many people are using this code?
1. The project was out on a farm. There was no jurisdictional authority requiring a permit or inspector. The county maintains that they do not require any code compliance on farms.
2. There was a hired erector but the farmer was acting as the coordinating entity in putting the pieces together. The farmer had a 4 year Construction Engineering degree (B.S.) but no design degree or experience.
3. 8 1/2 x 11 truss "shop drawings" were indeed prepared by the truss designer....using 20 psf live load in a Pg = 45 psf area. From his testimony, no unbalanced loading was used in the design software.
4. The failure, from my analysis, was definitely due to truss failure. I inspected all the trusses and found very good quality materials, nailing plates, bracing, bridging, etc. The actual snow load was definitely a drifting on the leeward side (6" deep on windward side and 30" on leeward). The metal roofing, the open terrain, the agricultural type, etc. were all included in my analysis.
The main issue is WHO is responsible for "catching" the 20 psf design in a 45 psf ground snow area (the unbalanced snow load on leeward side was 30 psf). The truss designer was asked "if you were asked to provide 20 psf trusses in a far northern area, near the Canadian border, would you question it?". He answered yes. In this case...at 45 psf, he didn't question it but just provided 20 psf.
Since The TPI and WTCA only seem to deal with the common "ideal" situation where there is an engineer/architect dictating loads, this situation seems out of the ordinary.
an unbalanced load case. If the software has the capability and the option has been suppressed, blame might shift toward the truss fabricator. Trusses more commonly fail due to improper erection & handling. With the actual load applied, does the CSI exceed a factor of safety of 2.5 for wood and 4 for steel? Have you determined the failure mode?
TruTrussEngineering@BuildersPost.com
The first end diagonal web member load was the first to be exceeded and this matched exactly the failed condition in the field.
The truss designer stated that the program did not use unbalanced loading in the design and my numbers seem to bear that out.
Item 1:
Although the county may have no requirements, does the state? In which case, is there a stipulated snow load?
Item 2:
A different level of technical expertize is expected from someone specializing in a type of work. What is the technical skill of the truss designer? Is he a certified technologist/engineer? Again, the greater skills, the greater the expectations.
This may also be a problem to the owner, since he may have the only technical 'credentials'.
I assume the owner has undertaken the coordination of the work: foundations general framing, etc. In the process he has put himself at risk; the work undertaken may not even be covered by insurance (I gather that there were no fatalities, only material damage). He has benefited from the reduced load (cheaper), the lack of professional input (also cheaper) and the lack of a general contractor (also cheaper).
Item 3:
The critical question is where did the 20 psf loading come from?
I've not experienced a snow loading that light; in our environs it's typically 35 psf and up. Is this a common or an unusual load for the area where the trusses are fabricated , where the lumberyard is located, or where the project is located?
Is it a common design load for ag buildings in any of those locations?
Our building code has reduced snow loading and no windloading for residential buildings; it's not uncommon for a truss supplier to run a truss not realizing that the building is commercial and, therefore, has a different loading criteria. If the truss design software had these features then as ctruax noted if the truss supplier switched these off, he may be accountable. Is the supplier equivocating when he says that the software did not use unbalanced loading for the design? or does the software have that feature and was it just disabled? A lot of the truss software is provided/rented by the truss plate suppliers and have an incredible number of features.
Did the lumberyard stipulate this loading to the truss fabricator? The reason for the question is that it's not common for a truss supplier to 'pick' a load out of the hat.
If the truss designer knew where the trusses were to be erected, and he selected the design load, then there is some negligence even if he provided shop drawings to the owner for approval.
If someone stipulated the design load, whether or not the truss supplier knew the location, then I would suggest that the truss supplier had a reduced duty of care to confirm it.
Has the truss supplier/designer provided trusses for the area where they erected, other than this job? If they (supplier or designer) had provided trusses for 10 projects in the area, they should have known.
What information is on the shop drawing? Did the owner sign it as being either reviewed or approved? Again a difference in the degree of acceptance. Was there any acceptance of the 20 psf live load? Was everything handled by phone, or was there a written contract of any kind?
The TPI or TPIC (in Canada) provides fairly good information/documentation, but lean towards the truss manufacturer as providing a material only. Other technical issues should be handled by the designer/professional/or someone else. Their guidelines (they actually have printed material) wrt to truss responsibility, fabricating, handling and installation are good and if followed will result in a 'successful' project.
I often provide copies of their erection and bracing information to clients with the usual disclaimers. I've also received copies of this information attached to shop drawings.
Have you determined the loading at the time of failure, not just the code stipulated loadings. What was the actual extent of snow on the roof? Have you run this on another 'roof truss program'?
Will add some material after I hear from my classmate.
Dik
Item 1 - No state requirment either.
Item 2 - The truss designer had a couple of weeks training on the software (from the vendor) and no formal engineering training. The farmer had the B.S. degree like I said..but no design experience. I'm sure he didn't know what a snow load even was.
Item 3 - The 20 psf came from the default on the software. Probably because south of Missouri/Kentucky the roof snow doesn't control design, but rather the roof live load of 20 psf.
The truss designer just took the order, "decided" himself to use 20 psf in the software (no one stipulated it) and designed the trusses. He knew where they went. He hadn't done a lot of trusses in the further north area before. The lumber yard was just the middle man.
The owner didn't accept the shop drawings,....he just erected them (which is a form of acceptance..but an ignorant one in this case).
The bottom line is: we engineers have a duty to protect the public welfare. Anyone else in the construction industry does not have this duty explicitly laid out as a foundation of their ethical behavior. In this case, the truss designer just used the "standard" LL on the trusses and sent them north to snow country. His job typically is supplying trusses dictated by someone else. In this case, the person asking for the trusses didn't know boo about snow load and a bunch of pigs had a shock.
Now that we know what happened, the reply is easy... If the truss supplier took it upon himself, without any guidance or direction whatsoever, to assign a live load or use the default out of ignorance, then I would suggest that the truss supplier is fully responsible for replacing their defective product... (it is not fit of purpose) and their responsibility could include any other damages sustained by the owner <G>.
The problem is that rarely are the supreme court justices unanimous...
BTW, your item 2 sounds very much like a concern I had about using FEM stuff just a while back...
Paragraph 2 just about sums it up... will get a copy of the *.pdf from the tpic site. Likely one similar is available from the tpi site in the US.
Message as follows:
Hello Dik;
The responsibiltie of various parties in TPIC opinion can be found in pdf format at tpic.ca
The responsibility is the supplier to verify that loading is correct for building location. Specified Ground snow load can be obtained from Environment Canada or local Bldg. inspector.
Farm trusses are required to be built to Part 4 with unbalanced , wind , & built up snow conditions. Farm code allows load sharing up to 4' O/C spacing as well as Importance factor of 0.8 for low human occupancy. Ontario Bldg. code regulates farm bldgs. using 1995 Farm code.
Vic Tanner P.Eng
Timber Systems Engineering Inc.
In most states, truss designs must be signed and sealed by an engineer. This is a "delegated" engineering function, secondary to the engineer of record responsibility. In this case, even if the owner was the "engineer of record", then the delegated function still must be done to accepted area standards. In this case the knowledgable party is the truss designer, so in my humble opinion, most of the responsibility lies there.
Ron
One last issue that occurs to me is that the truss supplier, whether he was responsible for setting the load or not, definitely had a responsibility to NOTIFY THE OWNER of the assumptions he made if there was no direct engineer of record. The owner was not cognizant of the risk he was taking by accepting, erecting and working under these trusses. The hog operation goes on...the pigs are still happy, but the farmer is out about $200,000.
(no pigs were injured in this event)
Is this a function of the truss supplier in some areas? What if there is no building permit or review process.
It appears that the jurisdiction where JAE is located is similar to this area. Neither a building permit nor an engineer is required for low occupancy farm buildings.
We usually spec that wood trusses be sealed and that the engineer be responsible for the design, fabrication and installation.
The Wood Truss Council of America has a *.pdf file titled "Standard Responsibilities in the Design Process involving Metal Plate Connected Wood Trusses"; document ref:WTCA 1-1995, prepared in conjunction with the TPIC.
A couple of key items;
1, under "Scope and Definitions"
"Truss Designer" is the design professional,individual or organization having responsibility for the design of metal plate connected wood trusses. The responsibility shall be in accordance with the state's statutes and regulation governing the professional registration and certification of architects or engineers. Also referred to as truss engineer, design engineer, registered engineer, and engineer, but hereinafter will be referred to as Truss Designer.
2, under 6.0 Truss Designer Responsibilities
6.1 Prepare the truss design drawings in conformance with the requirements set forth in the latest approved edition of "ANSI/TPI 1-1995, the 'National Design Standard for Metal Plate Connected Wood Truss Construction'", and
6.2.4 Design Loads as applicable
The above may be what Ron is suggesting... This, in conjunction with my earlier comment:
"If the truss supplier took it upon himself, without any guidance or direction
whatsoever, to assign a live load or use the default out of ignorance, then I would suggest that the truss supplier is fully responsible for replacing their defective product... (it is not fit of purpose) and their responsibility could include any other damages sustained by the owner <G>."
Unless the truss supplier is bankrupt, I would suggest the owner have another talk to them.
e.&o.e. <G>
If a tree falls in the woods and no one is around, does it still make a sound?!
The fact that it is a farm building and the local building department does not have a great interest, does not make it an invalid issue. That would be true if the farmer designed and built his own trusses for the building on
site and erected them; however, since the trusses were supplied for a building through a commercial venture, likely without regard to its permit status, the designer must bear the responsibility for the appropriate design without other specificity.
The answer to the second one, once all the information is out is also fairly simple, but not without pitfalls. My last message to JAE, summed it up... the owner should have a talk to the truss supplier regarding remedial work.
IMHO, the supplier of the trusses is responsible for making good, and for a variety of reasons (don't think the discussion has missed any). Having said that, the truss manufacturer may balk at the $200,000 ticket, his insurance may cover it, or because of "gross negligence" his insurance may not cover it. Because of this latter issue, the employee may be liable.
On the down side, the owner has technical training where no one else seems to; at very least, if he was in over his head, he should have known enough to seek other help. Had things not gone awry, the owner benefited from it financially. The owner was provided with a copy of the 'shop drawings' with the stipulated loads shown and accepted them (as pure supposition, truss shop drawings that I've encountered, usually have a couple of disclaimers). The problem is not 'clean'.
The only issue with respect to the building officials may have been, if they knew about it and did any type of inspection. As it stands, they were 'kept out of the loop' completely because there is no obligation to inform them (this would normally have been the constructor's or the owner's responsibility, anyway), there were no fees paid, and there was no contravention of laws, by-laws, or codes.
Just thought of it...
Just as an aside... I wonder what other trusses and what type of trusses this guy designed... could be a whole raft of them out there just waiting for some unsuspecting person...
In very rural counties, you do not have really anyone competent or interested in even looking at agricultural facilities, much less worry about code issues in design. This was the case here.
Ron - you're right that this lack of "authority" doesn't mean it isn't an important issue. Just means that now we have a situation where one side (the farmer) is claiming that the truss mfr. designed the trusses and is thus "THE DESIGNER" and the truss mfr claims (per TPI) that truss mfr's don't set the loading criteria and the farmer was managing all of the construction...therefore the farmer was "THE DESIGNER".
The mode of failure isn't the issue.
The inspection/code compliance isn't the issue.
The issue is: Who was the responsible designer.
The Canadian format seems to deal a little bit better with this nebulus situation where there is no Arch/PE involved; as opposed to the US situation where an Arch/PE/Competent designer-of-record is assumed to exist(TPI vs. TPIC).
In the absense of hard information, then it is necessary to establish what is generally recognized by the industry... You might want to obtain information from the WTCA and TPI about the number of members, and what other agencies are 'out there' for certification of plants. I would assume that the truss manufacturer must be certified by someone. Does this certifying (sp?) agency have any printed standards?
We've even heard of the WTCA and TPI in Canada, so they're International in scope <G>; their standards are likely representative of anyone that would certify the truss manufacturer. Another agency certifying the truss manufacturer may even make reference to the above agencies.
The definition of Truss Designer by the WTCA and the TPI states that "... The responsibility shall be in accordance with the state's statutes and regulation governing the professional registration and certification of architects or engineers...", is pretty heavy duty and encompassing. You might be able to use this definition to good purpose. The above information is from a document in *.pdf file format. If you send your email address to dikcoates@alpha.to, I'll forward a copy of it to you.
This would appear to tie them into accepting professional responsibility, even though they may not be professionals. It also provides a scope of responsibilities that is recognized by their industry.
Is the truss manufacturer a member of either of these groups? I'm not aware of any truss manufacturers here that are not members of the TPIC; is the truss manufacturer a member of the TPI?
Also, the truss designer responsibilities outlined in ANSI/TPI 1-1995 may have some bearing; I don't have a copy of this document, but it may have some useful information in it.
If the material can show what is nationally accepted, it may be helpful to the case.
Note that there seems to be a provision for the truss designer to be considered the Engineer of Record for the limited portion of the truss work, in the absence of a Project Structural Engineer of Record....
May 23, 2001
MEMORANDUM
BULLETIN G13-01
To: All Interested Parties
Chief, Building Inspection Division
Subject: Change to Rules Governing Truss Design Package
A recent change to Florida Board of Professional Engineers, Rules Chapter 61G15, Florida Administrative Code, regarding the design of structures utilizing prefabricated wood components, now permits, in the case of a truss design package, a cover or index sheet may be signed and sealed in lieu of signing and sealing each individual sheet, provided that the cover or index sheet contains the following information:
1. The name, address and license number of the Engineer of Record for the truss design package.
2. Identification of the project, name of the authority having jurisdiction (city/county), the loads, and the name date of the applicable building code that the truss design is intended to meet and all loads imposed on the structure.
3. Truss engineering design criteria with full identification of the source of the criteria. The source will be either the Engineer of Record (if there is an Engineer of Record for the structural engineering documents), or the engineer employed by the truss manufacturer. If there is an Engineer of Record for the structural engineering documents, that engineer shall be identified with his/her name, license number and address, along with a check mark to ensure that the drawings have been reviewed as required by Rule 61G15-30.006(3), F.A.C.
4. A truss layout plan by the Engineer of Record showing the location and designation of each component.
5. Identification of the computer program used for engineering the trusses.
6. An index of the attached drawings. The naming and numbering system utilized for the drawings shall be clear as to how many drawings there are in the set and the date of each of these drawings.
7. Each of these drawings in the package shall bear a title block bearing the printed name, address and license number of the Engineer of Record for the truss design and the date of the drawings.
If the above conditions are not met, then all sheets of the truss design package shall be signed, sealed and dated by the Engineer of Record for the truss design package.
Seals for either option shall be metal-type impression seals as per
61G15-23.001 F.A.C. (no wet or rubber stamp type seals permitted).
You have read too much into this letter. It does not deligate the responsibilities of the building designer to the truss designer. It simply says that the truss designer is not required to sign every page of the truss submittal package.
I suggest that everyone checking truss designs should read the commentary to WTCA 1-1995 (Similar to TPI 1-1995). Look on the web site www.Woodtruss.com under legislative issues.
We must always remember that the model building codes give the ultimate responsibility for conforming to the building code to the "permittee". This is defined as the building owner. They may hire professionals to perform this task, but if they choose not to hire professionals to do this, they take all risk into their own hands. I think you will find that all engineers who work in the truss industry would like professional engineers and/or architects to review all truss designs prior to fabrication.
While I agree that a permittee has the responsibility for code compliance in the construction, that does not mean that a construction permittee has the responsibility for design under separate law. If that premise were valid, then every contractor would have the responsibility to see that the Architects and Engineers of a project complied with the code in their designs. That is not the case. It is the engineer, whether or not there is an "official" engineer of record, who has a duty to meet the local standard of care in his practice. It is the engineer who is licensed, not the owner, nor the contractor.
Any resolution or court ruling?
Rick Kitson MBA P.Eng
Construction Project Management
From conception to completion
www.kitsonengineering.com
Y.S.
Before Wisconsin adopted the IBC 2000, I believe there was an exemption for agricultural buildings to be designed for 20 psf roof load. I do not know what the current regulation is.
I do not know what State your building is in, but Wisconsin is certainly considered a northern State.