Derating Cables in Water

Derating Cables in Water

Derating Cables in Water

(OP)
Hello.

Do cables that sit in water have to be derated?

The situation I am refering too, is where i have a submains cable that is installed underground in heavy duty conduit. The conduit is filled up with water completely and the water is not draining anywhere.
Should the cable current rating be derated?

Thank you.

RE: Derating Cables in Water

It depends. For low voltage, dual rated insulation the answer is yes. THHN/THWN is rated for 90C in air and 75C in water. For medium voltage cable, I don't think the ratings change, but you need to calculate the temperature rise based on the thermal conductivity of the surrounding material which is effected by water content.

RE: Derating Cables in Water

As alehman stated, if the cable has dual rated insulation, you need to limit the temperature to 75°C in wet locations.  The easy way is to derate according to NEC ampacity tables from 90°C to 75°C.  In reality, the fact that the conduit is filled with water will reduce the temperature for a given current because the thermal resistance of water is much lower than that of air.  To take advantage of this, however, you would have to use ampacities calculated under engineering supervision using Neher-McGrath's methods and the general formula shown in NEC 315.15(C).  This is not an easy task.  For medium voltage cable which isn't dual rated, you would normally ignore the cooling effect of the water in the conduit.  You can't depend on it being there at all times anyway.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources