I am working on  project that is using gensets to drive motors for centrifugal pumps and no-one is ready to recommend genset sizes.

Details
Motors are 127HP, 255Hp & 537HP @ 50Hz (all 380v)
Will be starated on digital soft staarters
Loads are centrifugal pumps.

Generators my client has "budgeted" for are
320KVA (256KW) PRIME, 50 HZ, 400 V FOR THE 127 HP MOTORS
500KVA (400KW) PRIME, 50 HZ, 400 V FOR THE 255 HP MOTOR
810KVA (648KW) PRIME, 50 HZ, 400 V FOR THE 537 HP MOTORS

I am not so concerned by the 255 & 127HP units but I feel that he has not allowed enough for the 537HP motor in terms of handling the inrush current, even allowing for the soft starter, at start up.

Any comments or recommendations?

Thanks

RE: Genset size recommendations

Call your catapiller Generator representative, they have software available or they will do the calc for you usually are no cost. They are typical of any generator company. If these are old generators they may do it for a fee.

IEEE also has starting voltage drop curve for generators with motor starting current. This in IEEE red book.

85 percent drop is the value that coils drop off for starters and relay so that is the maximum allow able drop for the motors. The motrr can drop off to 35 percent on starting and still work, but the coils for the motor controls will drop off before that kind on voltages are seen. This also limits the size of generator you can use.

There are more things to consider but this is a starting point.

good luck

RE: Genset size recommendations

Please refer to FAQ237-766.

Add you all initial loads and largest motor starting capabilities to it.

Hope this will help.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources