Underground Cables Installed but Left Denergized

Underground Cables Installed but Left Denergized

Underground Cables Installed but Left Denergized

(OP)
Our construction people want to install 15kV feeders underground, direct buried and leave them for approximately 9 months untill the equipment arrives.  The cables consist of corrgated aluminum armor with an outer PVC jacket.  The cables would be stubbed out at both ends and sealed.  They will be buried about 1500mm deep in a fine sand bed.  By doing this the constructors will complete the civil work sooner.  Anyone ever heard of any problems in doing this.

RE: Underground Cables Installed but Left Denergized


A perfect application for capped duct banks and pulling line.
  

RE: Underground Cables Installed but Left Denergized

I've used cables which sat unenergized for several years in similar installations.  But I would suggest you provide substantial mechanical protection where they exit the ground, particularly if it is a construction site. (IE concrete or heavy pipe guards)

RE: Underground Cables Installed but Left Denergized

I agree with busbar. Don't install the cables until you're ready to terminate them. If you must, leave them unterminated, leave several extra feet at each end and consult the manufacturer for instructions on sealing.

RE: Underground Cables Installed but Left Denergized

I too would strongly recommend empty duct banks rather than leaving unenergized cables sitting in the ground.  But if you are going to go the cable route and if you are using aluminum conductors, specify a filled cable.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources