CFM PERCENTAGES

CFM PERCENTAGES

CFM PERCENTAGES

(OP)
WHEN CHECKING FOR TOTAL SYSTEM AIRFLOW THE SYSTEM CFM RATING SHOULD BE WITHIN WHAT % OF THE FAN CFM RATING?

RE: CFM PERCENTAGES

Normal requirement is + /- 10% of design CFM at the terminals if a safety factor of minimum 10% was built in the load calculations. If not, use +15%/-0%. The CFM traverse at the fan will be greater than the sum of the CFM measured at the terminals because of leakage. Leakage of more than 10% is not allowable. Fan bhp equal or greater than motor hp or fan FLA more than design are not acceptable. Check for duct blockage.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources