Square D panelboard

Square D panelboard

Square D panelboard

(OP)
  For any of you electrical equipment distibutors or engineers. Does square D maunufacture 20 amp tandem single pole breakers for a NQOB panelboard ? Ravenjoe

RE: Square D panelboard

No, tandems are a residential device only.  That's why you see loadcenters with multiple circuit designations like 12/24 or 16/32. The higher circuit density is obtained with CTL type tandem breakers.  Lighting panelboards such as the NQOD/NQOB are strictly limited to the number of circuits they are nameplated for. Modification voids UL label and warranty.  

RE: Square D panelboard

(OP)
Thank you CHDean.

RE: Square D panelboard

(OP)
Could I install a subpanel ? This is a 100 amp panel. What size sub panel could I install.

RE: Square D panelboard

Absolutely, a sub-panel is definitely a solution. You will need to determine the total connected load of the existing panel to determine how much room is left for additional loads.  The panel you have will accept up to a 100A branch breaker to feed the sub-panel, you may need to relocate some existing loads to the sub-panel to make space for this breaker.

RE: Square D panelboard

If you have a hard time finding the information on the Square D site I will say that a 60-amp breaker is probably the largest you could or should put on the panel.  A 100-amp frame size is the next size up from a 60-amp frame and with very few exceptions would you be able to put a 100-amp branch breaker in a 100-amp panel.

RE: Square D panelboard

A 100A QOB should fit but you'd be using as a disconnect only as upstream device would react first in most situations.  If you use a smaller breaker you should acheive a better degree of coordination.  Without knowing loading, 60A would seem reasonable.

Red Flag This Post

Please let us know here why this post is inappropriate. Reasons such as off-topic, duplicates, flames, illegal, vulgar, or students posting their homework.

Red Flag Submitted

Thank you for helping keep Eng-Tips Forums free from inappropriate posts.
The Eng-Tips staff will check this out and take appropriate action.

Reply To This Thread

Posting in the Eng-Tips forums is a member-only feature.

Click Here to join Eng-Tips and talk with other members!


Resources