I want to know different between class x and other class in protection side?
When was the last time you drove down the highway without seeing a commercial truck hauling goods?
Download nowINTELLIGENT WORK FORUMS
FOR ENGINEERING PROFESSIONALS Come Join Us!Are you an
Engineering professional? Join Eng-Tips Forums!
*Eng-Tips's functionality depends on members receiving e-mail. By joining you are opting in to receive e-mail. Posting GuidelinesJobs |
|
RE: ct class x
http://www.nema.org
for National Electrical Manufacturers Association (NEMA) Standard 250 "Enclosures for Electrical Equipment (1000 Volts Maximum)" published in 1997
for more info. The only X appears at NEMA enclosure 4X to distinguish it from NEMA enclosure 4 since the NEMA 4X is corrosion resistant.
Also, visit
http://www.iec.ch
for International Electrotechnical Commission (IEC) Publication 529 "Classification of Degrees of Protection Provided by Enclosures"
for more info since the IEC enclosure and NEMA enclosures may be interchanged somewhat after a proper correspondence is established.
RE: ct class x
RE: ct class x
Suggestion: Reference:
1. ANSI/IEEE C57.13-1978 "An American National Standard IEEE Standard Requirements for Instrument Transformers"
Reference 1 addresses CT Classes on page 19. There are different CT Classes:
a) 5.3 Standard Accuracy Classes that are reflected in Table 6, i.e. 0.3, 9.6, 1.2 for Metering CTs
b) 6.4 Accuracy Classes for Relaying. There are essentially two Classes "C" and "T"
Which type of CTs do you have in mind?
RE: ct class x
The Class X CT is used for specific protection schemes, such as busbar protection, where a higher grade CT is required.
RE: ct class x
In Class X CT, u as the designer specify the knee point, to the manufacturer.
CT sec R, is also specicfed for the manufacturer.
He (or she) then generally processes all your class X CT orders form a single lot. This ensures that maximum similarity is maintained between the outputs of various CTs.
Generally Class X CTs are used in High Impedance Differential protection schemes. Where the fault behaviour of all CTs must be as exact as possible. esp in through fault conditions. In TFC the loaded CT tends to saturate, this is why the protection scheme designer 1st calculates the amount of through Fault current that is likely to flow and then works out a CT knee point that ensures linear range during max through fault conditions. In other words u try to ensure that your high impedance diff scheme will remain stable in case of Through Faults.
check out these documents:
http://www.geindustrial.com/pm/notes/ger3184.pdf
http://www.geindustrial.com/pm/notes/ger3961.pdf