I am wiring new restraunt and have 225A panel 3 PH, Load exceeds 80 Percent of rating. Plan checker susgested convert to power factor and it can go to full 225. Do you convert phase by phase or total panel load ? I noticed new code book calls out kVA and not watts as in older books. Is there a formular or do you just use Table
John
John






RE: Convert VA to Power factor for service panel,
Do you mean the actual current measured exceed the 80%rating of the breaker? (180A for a 225A CB)?
Per NEC you should NOT exceed 180A (80% of 225A) of continuous load (more than 3 hrs), regardless of the power factor.
If this is a calculaion then here are the formulas and you can calculate on your own:
V=line to line Volts, Amp=line current (each phase).
kVA = (1.732*V*A)/1000
kW= kVA*power factor (Assume 0.8 power factor if no other info is available).
If you calculated your loads in kVA, then you can find amps from the first formula. If you calculated your loads in kW, then you need to divide by the p.f. (0.8) to convert kW to kVA and then calculate the amps.
RE: Convert VA to Power factor for service panel,
Conductor heating is generally a current-based function, so, for instance, using kW-demand history may undersize the proposed equipment. Panelboards don’t care what the load PF is, and voltampere figures consist of real- and reactive-power components.
Voltampere-demand checks will produce larger {or equal, but not smaller} numbers compared to watt-demand measurements, for more safely sizing electrical-distribution equipment.
RE: Convert VA to Power factor for service panel,
RE: Convert VA to Power factor for service panel,
Watts = Volts·Amps·Power Factor
You would have to add capacitors to increase the power factor.
Volts·Amps = sqrt(Watts²+(Reactive Load vars - Capacitor vars)²)
With these two equations and some algebra you should be able to figure out how many capacitor vars you need. Keep in mind that you can calculate the Reactive Load vars from the second equation with zero Capacitor vars. I doubt that it would be less expensive than installing a larger panel and conductors, however.
RE: Convert VA to Power factor for service panel,
I have done a lot of restraunts and 225 amps panel is usually just to small an amperage. However use the examples for shown in the NEC code for sizing your load not just 80 percent. If you don't know how to use them hire someone that does to train you- like an master electrician or a professional engineer.