Here is the situation. We have a monorail system (35ft span 5 Ton capacity) supported at both ends into the main building structure and by 8 anchor points welded to the main horizontal roof trusses. It has been in operation for 10 years plus and there is no sign of corrosion or cracking or yielding (paint is still like new).
Now here is the problem. A crane inspector had reservations about the 8 bracket anchor points. These are square tubing (2"x2" assuming 1/4" thickness and 7" long) welded between two 1/2" plates where the bottom is mounted to the main horizontal I-beam (w12x26) with 4 - 3/4" grade 5.2 bolts (Sp=85 Kpsi) and the top is welded to the roof trusses. We had multiple inspectors on site inspect our cranes and this is the first time that this was brought up. The square tubing seams to have been installed at an angle from that start with the bottom being flat with the I-Beam and the top being mounted at a small angle to the roof trusses.
Brackets looks like this:
____
There is approximitly 1/2" difference between the top and bottom and seems have been pre-bent or bent during installation.
I have gone through stress calculations for the welds, bolts, beam and tensional stresses in the square tubing.
All ok.
My question is what is the best way to calculate the square tubings stress with the bend in it.
Echan
____
All ok.
Echan
RE: Monorail support system problems
if you want to calculate, here is my suggestion:
the bent puts eccentric load which mean bending monent of [force]x[eccentricity] on the rectangular strut. calculate both the strut and the fillet weld to the plates for this moment.
zvi